I'm trying to get a wall hung toilet installed in my condo but failed permit review because as I understand it, the wet vented drain for the WC has to be at the same elevation or lower than other wet vented plumbing group fixtures such as the shower.
Review Comment: "Bathroom, relocated toilet, not as per FBC 912.1.1, (other fixture drains shall connect at same of above WC elevation, see SH)"
Code Reference: https://codes.iccsafe.org/content/FLPC2023P1/chapter-9-vents#FLPC2023P1_Ch09_Sec912
I'm on the top floor of the building and have 26 showers below my WC so I am thinking it must be possible using the right venting for the shower which might be different for the showers below me since they are allowed to be under a WC.
Could adding a (dry?) vent for the shower (see red dashed line in drawing) that connects above the lavatory/sink which is the last fixture connected before what would considered the dry vent(?) (where the existing vent stack from units below also connects) fix the issue? This way the shower vents above the WC? or is there another (better/right) way of doing it?
(shower drain is 1-1/2" and not 2" as indicated).
Hope someone out there can help.
Review Comment: "Bathroom, relocated toilet, not as per FBC 912.1.1, (other fixture drains shall connect at same of above WC elevation, see SH)"
Code Reference: https://codes.iccsafe.org/content/FLPC2023P1/chapter-9-vents#FLPC2023P1_Ch09_Sec912
I'm on the top floor of the building and have 26 showers below my WC so I am thinking it must be possible using the right venting for the shower which might be different for the showers below me since they are allowed to be under a WC.
Could adding a (dry?) vent for the shower (see red dashed line in drawing) that connects above the lavatory/sink which is the last fixture connected before what would considered the dry vent(?) (where the existing vent stack from units below also connects) fix the issue? This way the shower vents above the WC? or is there another (better/right) way of doing it?
(shower drain is 1-1/2" and not 2" as indicated).
Hope someone out there can help.