is this legal?

Help Support Plumbing Forums:

Umatt322

Member
Joined
Jun 20, 2020
Messages
13
Reaction score
0
Location
Nj
Tjan
1. UPC: Vertical wet venting is limited to (1) one and two (2) fixture unit fixtures.
You are currently showing a vertical venting of three (3) fixture units into the WC drain.
;)
But even if the shwr and lav are already vented before they tie into the vertical drain?
If that is true can't I just vent the WC off of it's horizontal drain individually?20200622_124656.jpg20200622_124656.jpg20200622_124656.jpg
 
Last edited:

breplum

Professional
Professional
Joined
Nov 14, 2017
Messages
447
Reaction score
152
Location
Lafayette, CA
Certainly if you vented the WC like you show in red, it would comply in every way I can imagine.
BTW, we are arguing technicalities. Even without the dedicated WC vent, the reality is that parallel users at the double lav would be inconsequently rare and all plumbing design is robust by default so it would all work fine in my view.
 

Umatt322

Member
Joined
Jun 20, 2020
Messages
13
Reaction score
0
Location
Nj
Certainly if you vented the WC like you show in red, it would comply in every way I can imagine.
BTW, we are arguing technicalities. Even without the dedicated WC vent, the reality is that parallel users at the double lav would be inconsequently rare and all plumbing design is robust by default so it would all work fine in my view.
I actually really enjoyed the conversation. Thanks again for giving me insight on the plumbing venting code.
 