You may have a problem between the meter and the house. I had over 90-psi static pressure, which dropped to around thirty with one fixture running. The sixty feet of 3/4-galvanized steel between the meter and the house, had enough chancer on the interior that the friction loss was huge.
Replaced it with pex in a poly sleeve, and the problem was solved.
So, do you have any steel pipe which could be corroded on your system? Or, any other lines that could be pinched or deformed?