3.5-year-old 3500 square foot residence, 2.5 bath
I’m having an issue with my Watts LF25AUBZ3 (3/4”) PRV causing excessive pressure fall at relatively low flow rates. The service side is a steady 75 PSI. I have the house side set to 50 PSI static. When I flow 10 GPM, the house side drops to 25 PSI. The supply side stays at 75 PSI, indicating that I do not have a supply problem.
My setup is shown in the pic below.
I checked the strainer in the PRV, it is clean.
This is my second LF25AUBZ3 in only 3 years. The first one was unable to hold pressure even in a static state.
I am thinking about reconfiguring the setup to accommodate a Zurn 500XL3, which I suspect is a significantly higher quality PRV. On paper, its pressure fall is much less than that of the Watts. I am also thinking about switching to a dual-pressure system: 50 PSI regulated for the house, 75 PSI unregulated for the hose bibs.
I would adapt the current ¾” supply to 1” and install a 1” LF7R backflow preventer. I would then do a 1” + ¾” branch. 1” for the Zurn LF25AUBZ3 (the smallest size it comes in) and ¾” for the hose bib manifold.
Note that my Watts LF7R backflow preventer is currently downstream of my PRV. It would be moved upstream.
Does this all sound like a good idea? Am I missing anything?
Feedback and/or telling me I’m crazy is welcome.
Thanks.
I’m having an issue with my Watts LF25AUBZ3 (3/4”) PRV causing excessive pressure fall at relatively low flow rates. The service side is a steady 75 PSI. I have the house side set to 50 PSI static. When I flow 10 GPM, the house side drops to 25 PSI. The supply side stays at 75 PSI, indicating that I do not have a supply problem.
My setup is shown in the pic below.
I checked the strainer in the PRV, it is clean.
This is my second LF25AUBZ3 in only 3 years. The first one was unable to hold pressure even in a static state.
I am thinking about reconfiguring the setup to accommodate a Zurn 500XL3, which I suspect is a significantly higher quality PRV. On paper, its pressure fall is much less than that of the Watts. I am also thinking about switching to a dual-pressure system: 50 PSI regulated for the house, 75 PSI unregulated for the hose bibs.
I would adapt the current ¾” supply to 1” and install a 1” LF7R backflow preventer. I would then do a 1” + ¾” branch. 1” for the Zurn LF25AUBZ3 (the smallest size it comes in) and ¾” for the hose bib manifold.
Note that my Watts LF7R backflow preventer is currently downstream of my PRV. It would be moved upstream.
Does this all sound like a good idea? Am I missing anything?
Feedback and/or telling me I’m crazy is welcome.
Thanks.