The aav would pass in my jurisdiction. Two wax is right there’s a possibility of positive pressure causing an issue but you won’t know for sure until it’s in use. I expect it would work fine.Got it. Thank you! So something like the attached picture with my scribble. Can I vent to the side of the house or does it have to go to the roof? Alternatively, can I use an air admittance valve like the second picture instead?
I might would try a studor but if the studor didn’t work I’d try to find one of those pipes that didn’t have a toilet flushing through it and use it as a vent. But it wouldn’t pass code.
If you’re correct and the basement bathroom is vented through the roof, you should be able to connect to that vent assuming it’s in proximity to the new laundry.Thanks. I'm on a public sewer system, not septic, so at least I have that going for me. I'll still try to find a way to connect to the dry went, but it looks like it will require drywall demolition on the first and/or second floor.
The basement bathroom I mentioned must also be connected to that dry vent somehow. It was part of the house during initial construction and the house is a 2015 build. I'm assuming I should be able to connect through there somehow.
@Twowaxhack What if I moved my cleanout lower and then lowered the other two branches and tapped into that line above the other 3" branch? Wouldn't this significantly mitigate my positive pressure risk? Something like the attached?View attachment 41205
Wow, this is amazing. Thank you for the insight. I will report back!As others have said, an AAV is allowed in their jurisdictions. Twowaxhack brings up the real issue of where an AAV has its problem and some jurisdictions do not address. The AAV is a one-way valve, whereas an atmospheric vent allows air flow both ways. So, if any positive pressure develops in the plumbing system, especially like in multi-story buildings, the pressure has to find its way out from the downstream plumbing.
So, if AAVs are allowed in your jurisdiction and they do not have any asterisks by their allowance, and if they do not restrict washing machines to be installed at the base of a stack, here is an idea that would resolve the positive pressure issue and I believe would be acceptable per code.
Install a 2" reducing wye below the AAV and run a 1 1/2" or even 1 1/4" line to the vertical line you said had hot water flowing in it from a sink. Install it as high as practical. Use a Sanitary tee for that connection. That vent line would likely provide the venting of any positive pressure that may occur.
You asked earlier if you could vent through a wall instead of through the roof. Yes, you can with the following restrictions. These are IPC, but UPC is pretty close as well.
Section 903 Vent Terminals
903.5 Location of vent terminal.
An open vent terminal from a drainage system shall not be located directly beneath any door, openable window, or other air intake opening of the building or of an adjacent building, and any such vent terminal shall not be within 10 feet (3048 mm) horizontally of such an opening unless it is 3 feet (914 mm) or more above the top of such opening.
903.6 Extension through the wall.
Vent terminals extending through the wall shall terminate at a point not less than 10 feet (3048 mm) from a lot line and not less than 10 feet (3048 mm) above average ground level. Vent terminals shall not terminate under the overhang of a structure with soffit vents. Side wall vent terminals shall be protected to prevent birds or rodents from entering or blocking the vent opening.
Seems like that Red Pipe is actually serving 2 Full Bathrooms from the second floor. So two toilets are flushing down that pipe.Make sure a toilet doesn’t flush down the pipe you marked in red.
Install a 2" reducing wye below the AAV and run a 1 1/2" or even 1 1/4" line to the vertical line you said had hot water flowing in it from a sink. Install it as high as practical. Use a Sanitary tee for that connection. That vent line would likely provide the venting of any positive pressure that may occur.
You asked earlier if you could vent through a wall instead of through the roof. Yes, you can with the following restrictions. These are IPC, but UPC is pretty close as well.
Section 903 Vent Terminals
903.5 Location of vent terminal.
An open vent terminal from a drainage system shall not be located directly beneath any door, openable window, or other air intake opening of the building or of an adjacent building, and any such vent terminal shall not be within 10 feet (3048 mm) horizontally of such an opening unless it is 3 feet (914 mm) or more above the top of such opening.
903.6 Extension through the wall.
Vent terminals extending through the wall shall terminate at a point not less than 10 feet (3048 mm) from a lot line and not less than 10 feet (3048 mm) above average ground level. Vent terminals shall not terminate under the overhang of a structure with soffit vents. Side wall vent terminals shall be protected to prevent birds or rodents from entering or blocking the vent opening.
I'll answer #2 first.1. Given there are two full bathrooms flushing and draining to that red pipe, is that still a good option to use for the positive pressure vent? Or should I use one of the other 3" pipes that have less load (maybe the half bath one in green).
2. Since this is an exterior wall, wouldn't adding a new vent directly to the outside be easier by going through the wall. My house does have soffit vents. The code says it can't terminate under the overhang of a structure with soffit vents. Does that mean it can't terminate anywhere underneath it even if that soffit is 30 ft high? There are no openable windows or doors on this side of the house and the roof is at least 30-40 ft off the ground.