Sewage pump cycling

Plumbing Forums

Help Support Plumbing Forums:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

Barry newman

New Member
Joined
May 28, 2019
Messages
1
Reaction score
0
Location
Huntsville ontario
Hi, my lower bathroom has a pump up automatic sewage pump that kicks in every 2 hours. (not consistent )or so when bathroom not in use, flapper dousnt appear to be leaking.any suggestions ? Thx.
 
Hi, my lower bathroom has a pump up automatic sewage pump that kicks in every 2 hours. (not consistent )or so when bathroom not in use, flapper dousnt appear to be leaking.any suggestions ? Thx.
Is the pump pumping up a distance before dumping into a gravity line?
For example, if the pumps discharge line has enough liquid in it, which is being held back a check valve, and the check valve is not holding, it's possible that the volume that is typically in the discharge pipe is leaking back slowly and causing the pump to pump it again and again.

EDIT:...

LENGTH_____PIPE SIZE____GALLONS WATER
1 FOOT_______2 INCH_________0.1356
1 FOOT_______2 1/2 INCH_______0.2120
1 FOOT_______3 INCH_________0.3053
1 FOOT_______4 INCH_________0.5426
 
Last edited:
do you have a dehumidifier or a condensate drain ??????shut the water off to all the fixtures you think drain into it and see what happens....if you have to shut off the water to the whole house if you need to
 