G Gh0st Member Joined Aug 14, 2017 Messages 18 Reaction score 1 Location , Sep 1, 2020 #1 Is there anything in new mexico upc that says a sand interceptor vent cannot tie into sanitary sewer vent?
Is there anything in new mexico upc that says a sand interceptor vent cannot tie into sanitary sewer vent?
breplum Professional Professional Joined Nov 14, 2017 Messages 2,374 Reaction score 1,210 Location Lafayette, CA Sep 1, 2020 #2 Should be fine. All traps/interceptors are considered in the same basic category. And vents, when connected to other vents, just must be tied in 6" above the flood rim of the highest fixture.
Should be fine. All traps/interceptors are considered in the same basic category. And vents, when connected to other vents, just must be tied in 6" above the flood rim of the highest fixture.
G Gh0st Member Joined Aug 14, 2017 Messages 18 Reaction score 1 Location , Sep 1, 2020 #3 Yeah just checking with you all i got a pipefitter from pennsylvania telling me this.He cant plumb for ****
Yeah just checking with you all i got a pipefitter from pennsylvania telling me this.He cant plumb for ****