Raising the vent up higher was a good idea, but generally a vent pipe should not run horizontal until it is 6" above the flood level rim. You can get away with having an AAV terminate below the flood level so long as it is at least 4" above the trap weir (but generally, you want to get it as high as possible, but also have the pipes as vertical as possible). When I was trying to figure out how to vent my sink I was told to use 45s instead of 90s to offest the vent slightly. First 45 would be right above where it comes out of the top and after diverting a bit over to the side, another 45 would make the pipe run straight up again just below the AAV. (I think it was 45s, might have been 1/8th bends but my memory is sucking today)
I'm not sure if having the 90s will be a problem or not though. Also, AAVs are generally designed for city sewer systems and sometimes the gases from a septic tank can blow the diaphragm in an AAV, so keep your nose open for sewer gas smell in case it does go.
Hopefully this will solve the problem though. The solvent weld parts (the ones that don't connect with the nut that twists on to hold them in place) need to be glued (but the AAV itself doesn't need to be glued, it can just thread in for easier replacement). If you haven't glued them already, you may be able to return the 90s and get 45s instead (or you can keep the 90s for future projects).
Diehard is right that you will need room to unscrew the AAV should it need to be replaced.
Disclaimer: I am not a plumber, but I've tried to learn what I can from the actual plumbers here. Frodo is the one who usually pipes in with the best answers (pun intended).