Yeah, I have the blue one in the photo above.
So, when the pump is off and therefore not circulating water, doesn't it have a relatively good amount of pressure drop across it with the water flowing through the pump housing and turning the unpowered impeller?When it’s off it can’t circulate the water
Yeah that like looks like a nice one. So you were right. Got home took out check valve. Luckily it was just a push connect one. Sure enough I was able to blow air both ways. Than a small piece of what I'm assuming is a small piece of my water heater fell out. Now air only passes one way. Thanks so much everyone for the help, top notch! Hopefully showers better tonight.
Nice test, but that does not replicate the conditions of the installation.View attachment 41911View attachment 41912View attachment 41913View attachment 41914
It took a little over 2 seconds longer to fill a 5 gallon bucket flowing through the pump. Pump was not running for either test.
That’s about 10 gpm. I think that’s plenty
That really does make sense. I was not aware that the pump restricted flow that much. I will install it on either side of the check valve and give that a go. Thanks for the replies. Really appreciate it.
this is great thanks. I was wondering if there was any flow restrictions but it doesn't look to be anything noticeable. Thanks for dropping a lot of knowledge on me. Appreciate all the time you took.View attachment 41911View attachment 41912View attachment 41913View attachment 41914
It took a little over 2 seconds longer to fill a 5 gallon bucket flowing through the pump. Pump was not running for either test.
That’s about 10 gpm. I think that’s plenty
I wonder what that does to the dynamics of the water heater, with a constant mixing of the tank.
And if the pump isn't running 24/7 how does it get turned on... by a timer of some sort?
I used a smart plug on mine and it can be activated by voice as well. It's scheduled to run in the morning every 30 mins for 3 mins for around 2 hours. Now that I've got my check valve issue fixed it's working really well. Before this it took me almost a minute to get hot water upstairs so I assume I'm saving some money on water.I wonder what that does to the dynamics of the water heater, with a constant mixing of the tank.
And if the pump isn't running 24/7 how does it get turned on... by a timer of some sort?
This is really good to know. At first I thought there was a flow issue and the volume of cold water was a lot greater than that of the hot.I ran more tests. 2 gallons a minute at 50psi with the pump and without. With that flow rate there was virtually no difference in time to fill the bucket or pressure drop that I could measure.
I also jammed the impeller with a piece of wire coat hanger. No change at 2gpm flow rate.
This is really good to know. At first I thought there was a flow issue and the volume of cold water was a lot greater than that of the hot.
Your test is still not legitimate. You are using the entire 50 psi available across the stopped pump. You need to add pipe, a manifold, more pipe, and a shower head after the stopped pump and see the impact to the flow at the shower head. Each of those items need to have pressure as a motive force for the water to flow.I ran more tests. 2 gallons a minute at 50psi with the pump and without. With that flow rate there was virtually no difference in time to fill the bucket or pressure drop that I could measure.
I also jammed the impeller with a piece of wire coat hanger. No change at 2gpm flow rate.
Your test is still not legitimate. You are using the entire 50 psi available across the stopped pump. You need to add pipe, a manifold, more pipe, and a shower head after the stopped pump and see the impact to the flow at the shower head. Each of those items need to have pressure as a motive force for the water to flow.
Yep, I haven't heard any complaints from the wife so I'm assuming we're all good now,I've got hot water everywhere and temps are stable.I checked flow at 80 psi,65 psi, 50 psi and 40 psi. During flow and static.
The flow rates at lower pressure were basically the same.
I had a hose valve creating back pressure on the pump and a pressure gauge.
I jammed the impeller.
Basically no measurable change.
All that PLUS the manufacturer allowing it to be installed in the flow while the pump is running and when it’s not running…….tells me that I have a person who is attempting to make a convoluted wreck of a thread for nothing.
The OP has been helped and we found a check valve that wasn’t closing. Problem solved.
Adding restrictions such as piping, manifolds is useless. Everyone’s house is different and we’re just checking the loss through the pump not an entire plumbing system.
Plus everyone who has this pump says their flow has not been affected.