Hello,
I'm adding a kitchenette to my basement and am getting confused on the code requirements for connecting my sink drain. I have an existing 2in horizontal drain underfloor that runs from the vented soil stack up the back wall (see photo) to the main floor kitchen sink. This kitchen sink does not have a roof vent and instead uses an AAV. I am looking to connect a basement kitchen sink to the vertical 2in. I understand you can't wet vent between floors, but does my proposed plumbing connection of adding a sanitary tee and new horizontal branch arm then venting this with an AAV before the sink rough in connection allowable? And would the downstairs sink AAV need to be above the flood level of the upstairs sink or just the downstairs sink? I know it would need to be accessible. Thanks!
I'm adding a kitchenette to my basement and am getting confused on the code requirements for connecting my sink drain. I have an existing 2in horizontal drain underfloor that runs from the vented soil stack up the back wall (see photo) to the main floor kitchen sink. This kitchen sink does not have a roof vent and instead uses an AAV. I am looking to connect a basement kitchen sink to the vertical 2in. I understand you can't wet vent between floors, but does my proposed plumbing connection of adding a sanitary tee and new horizontal branch arm then venting this with an AAV before the sink rough in connection allowable? And would the downstairs sink AAV need to be above the flood level of the upstairs sink or just the downstairs sink? I know it would need to be accessible. Thanks!