Not sure we're on the same page... Here is a pic of the pvc that goes to the grinder/sump across the basement, probably 15' under ground.
https://photos.app.goo.gl/skWmxgEf93CC27LEA
Here is another view from the top
https://photos.app.goo.gl/b9SMUPEbwYTHY8418
If I put a coupler on this then a PTrap with the drain for shower on the other end of the ptrap, should that drain be flush with the ground, slightly below (like the first picture showing the PVC a couple inches under the concrete), or slightly above ground level.
https://photos.app.goo.gl/skWmxgEf93CC27LEA
Here is another view from the top
https://photos.app.goo.gl/b9SMUPEbwYTHY8418
If I put a coupler on this then a PTrap with the drain for shower on the other end of the ptrap, should that drain be flush with the ground, slightly below (like the first picture showing the PVC a couple inches under the concrete), or slightly above ground level.
Depending on the levelness of your basement floor, you could be right. But the dimensions you've provided don't compute.
From your earlier posts/answers, the line into your sanitary sump is 3" and runs about 12 feet from your toilet. While I like to run 3" at 1/4" per foot slope, some codes allow 1/8" per foot. The minimum fittings for a toilet, a street 90 and a toilet flange, measure 5" from the top of the flange to the centerline of the horizonal pipe, or 3 1/4" to the top of the pipe. Using the 1/8" slope, that's 1 1/2" for 12 feet. So that would put the bottom of your toilet about 6 1/2" above the top of the pipe entering your sanitary sump. But that's a LOT of slope for a basement floor!
Sound like you need additional investigation of the piping.