P-traps after flushing fixtures

Plumbing Forums

Help Support Plumbing Forums:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

matt.mena

Well-Known Member
Supporting Member
Joined
Feb 12, 2021
Messages
249
Reaction score
187
Location
Charlotte
I was corrected by my NC county plumbing inspector on the proper way to vent this floor drain.

D7424091-2F35-4136-BC4F-92E90DC4BBC0.jpeg

Even if I change the 4” combo to a sweep and throw in a horizontal 4x3 wye to catch the floor drain, the p-trap is still not protected from the toilet discharge syphoning the p-trap.

79AB40A4-72B8-49B0-A7DA-F3CD4915BE01.jpeg

“In a perfect world would it syphon? Probably not. Reguardless, the codes must be met.” says my inspector. We’ve actually become friends over the years.

Luckily the floor drain fixture branch travels under the chase. I will install a 3x2 combo for dry vent looking straight up. Dry vents must remain vertical (45-90 degrees) until it is 12” above the flood level rim of fixture. (I think it’s 12”, correct me if I’m wrong, just too lazy to go look it up right now)

Even my field supervisor got this wrong.

Thanks TW, checking with my inspector is definitely the way to go. No wasting time installing something incorrect.
 