Default Toilet Vent and Wall Size

What size pipe does a toilet vent require and can a toilet be plumbed against a wall with 3.5" studs

Thanks



__________________
rcspott is offline  
 
Reply With Quote Quick reply to this message
Old 05-18-2012, 06:23 PM   #2
desertwater
Member
 
desertwater's Avatar
 
Join Date: Jan 2012
Posts: 86
Default

Toilet vent min. Is 2" however you need a full size cleanout before you can reduce to 2" if this is a second floor application you could flat vent a toilet with 2". cleanouts are not required on second floors (residential). and no 3" will not fit in 2 x 4 wall unless its steel stud.



__________________
desertwater is offline  
 
Reply With Quote Quick reply to this message
Old 05-18-2012, 10:44 PM   #3
phishfood
Moderator
PLF_MODERATOR.png
 
Join Date: Jan 2010
Location: Orlando, FL
Posts: 4,385
Liked 477 Times on 389 Posts
Likes Given: 638

Default

That is very much dependant upon which code is in use in your area.

In my area, 1/2 the diameter the drainage pipe served, minimum drain for a toilet is 3", so 1 1/2", with at least one 2" diameter vent for each sewer connection.

__________________

Lake County, Florida plumber
Springtime Plumbing Services, LLC
License #11067533
352-630-5673

phishfood is online now  
 
Reply With Quote Quick reply to this message
Old 05-18-2012, 11:50 PM   #4
HoffmannFamilyPlumbing
Plumbing Expert
 
HoffmannFamilyPlumbing's Avatar
 
Join Date: May 2012
Location: San Luis Obispo, CA
Posts: 6
Default

Depends which code your state adheres to. The International Plumbing Code (IPC) is 1 1/2" but the Uniform Plumbing Code (UPC) is 2"

__________________
http://hoffmanplumbing.net/
Hoffmann Family Plumbing
805-748-4324
HoffmannFamilyPlumbing is offline  
 
Reply With Quote Quick reply to this message
Old 05-18-2012, 11:56 PM   #5
johnjh2o
Senior Member
 
johnjh2o's Avatar
 
Join Date: Jul 2011
Location: Melbourne, Florida
Posts: 2,558
Liked 397 Times on 318 Posts
Likes Given: 253

Default

Quote:
Originally Posted by desertwater View Post
Toilet vent min. Is 2" however you need a full size cleanout before you can reduce to 2" if this is a second floor application you could flat vent a toilet with 2". cleanouts are not required on second floors (residential). and no 3" will not fit in 2 x 4 wall unless its steel stud.
3" pipe WILL fit in a 2x4 wall but the fittings will not. And you can not run a flat vent below the flood rim of the fixture unless it is washed by a fixture.

John
__________________
johnjh2o is offline  
 
Reply With Quote Quick reply to this message
Old 05-19-2012, 01:52 PM   #6
desertwater
Member
 
desertwater's Avatar
 
Join Date: Jan 2012
Posts: 86
Default

John, the toilet being flushed is washing the vent. no?

__________________
desertwater is offline  
 
Reply With Quote Quick reply to this message
Old 05-19-2012, 03:06 PM   #7
johnjh2o
Senior Member
 
johnjh2o's Avatar
 
Join Date: Jul 2011
Location: Melbourne, Florida
Posts: 2,558
Liked 397 Times on 318 Posts
Likes Given: 253

Default

If the vent runs horizontal below the toilet there is no way that the toilet could wash it. There may be a small amount of water that will enter the vent but that is the problem. If the line is not being washed the vent could become plugged from waste being left behind in the vent. If the vent was being washed from above like in the case of a lav being armed off the vent it would be fine. No vent can be run horizontally unless it is 6" above the floor rim of the fixture.

John

__________________
johnjh2o is offline  
 
Reply With Quote Quick reply to this message
Old 05-19-2012, 03:47 PM   #8
desertwater
Member
 
desertwater's Avatar
 
Join Date: Jan 2012
Posts: 86
Default

This is how I see it.

Click image for larger version

Name:	ForumRunner_20120519_084656.jpg
Views:	807
Size:	8.4 KB
ID:	2607

__________________
desertwater is offline  
 
Reply With Quote Quick reply to this message
Old 05-19-2012, 03:52 PM   #9
johnjh2o
Senior Member
 
johnjh2o's Avatar
 
Join Date: Jul 2011
Location: Melbourne, Florida
Posts: 2,558
Liked 397 Times on 318 Posts
Likes Given: 253

Default

The top one is wrong unless there is a fixture draining into the 2" vent above the toilet. The second on is correct you have no horizontal vent lines.

John

__________________
johnjh2o is offline  
 
Reply With Quote Quick reply to this message
Old 05-19-2012, 03:55 PM   #10
desertwater
Member
 
desertwater's Avatar
 
Join Date: Jan 2012
Posts: 86
Default

Ive done a lot of messed up plumbing then :/



__________________
desertwater is offline  
 
Reply With Quote Quick reply to this message
Reply


Quick Reply
Message:
Options

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Bathroom vent through wall? Dozey Plumbing Building Code 1 07-22-2011 12:31 PM
toilet vent running horizontal alainmax Plumbing Building Code 11 06-17-2011 06:05 PM
vent size tabrizi General Plumbing Help 0 11-08-2010 03:44 AM
Saniplus pumping toilet vent? dan0 General Plumbing Help 1 03-30-2010 02:00 PM
**Wall mount toilet for residetial** PAGEINC13 Toilets and Sinks 5 02-17-2010 03:01 PM