Default snaking drains of apartment building

All, TIA for advice. I work in a 6 floor apartment building and we're doing a routine maintenance snake of the tiers of kitchen drains. The plumbing company is suggesting they need to snake every unit on every floor, but I would think they would only need access to each of the top floor units and can snake the whole tier from there (and thus not need access to all the lower units that feed the same drain lines). Is the plumber correct for some reason I'm not considering or is he simply trying to bill me to needlessly snake every unit?

Also, if the drains are all one and quarter inch pipe, is that the size of snake that'd ideal be used? I believe they're suggesting the use of a three quarter inch snake, which seems undersized. Again, I'm concerned they might just be trying to use a three quarter so we have to use them again sooner and shell out for the job again.

Finally, how often would everyone recommend we have the snaking done? Every year? Every 3? Every 5?

In summary - do we need to snake every unit, how often, and what size snake. Thanks for the advice.



__________________

Last edited by bobv; 04-01-2014 at 04:48 AM.
bobv is offline  
 
Reply With Quote Quick reply to this message
Old 04-01-2014, 04:53 AM   #2
journeyman
the professional
 
journeyman's Avatar
 
Join Date: Oct 2012
Location: san diego, california
Posts: 278
Liked 87 Times on 68 Posts
Likes Given: 87

Default

I use a spartan 100 machine on kitchen lines. Belive the cable is 3/8. The cable i have is also 75 feet long. If you have 6 floors at 10 feet a floor 70 feet of cable will be plenty. I am assuming the kitchens are all on the same stack. He wants to run each floor so he can charge you more and cable is less work to get back. You run 70 feet of cable gravity pulls on it and it is hard to pull back. You always want to run a cable as far as you can in a building like yours. It is possible to push a clog to the next floor causing a flood. Cabling the line is only going to puch a hole through clogs. Hydro jetting gets the line clean and pushes all the debris out of line. It can be messy though if done on inside of unit



__________________
journeyman is offline  
bobv Likes This 
Reply With Quote Quick reply to this message
Old 04-01-2014, 06:00 AM   #3
bobv
Junior Member
 
Join Date: Apr 2014
Posts: 3
Likes Given: 1

Default

Thanks, journeyman. In theory, does it make sense that the hydro jetting could be done via the roof vents (so water isn't being sprayed in the top floor units)? That's assuming each drain stack has it's own vent, which I would imagine is the case....

__________________
bobv is offline  
 
Reply With Quote Quick reply to this message
Old 04-01-2014, 12:52 PM   #4
johnjh2o
Senior Member
 
johnjh2o's Avatar
 
Join Date: Jul 2011
Location: Melbourne, Florida
Posts: 2,683
Liked 466 Times on 366 Posts
Likes Given: 335

Default

If the line is snaked from the top floor he will clear the vertical line. But there may be horizontal waste arms that need to be done from under each sink.

__________________

John

johnjh2o is offline  
2
People Like This 
Reply With Quote Quick reply to this message
Old 04-01-2014, 01:28 PM   #5
IFIXH20
HERE TO HELP
 
Join Date: Mar 2012
Posts: 926
Liked 229 Times on 180 Posts
Likes Given: 163

Default

Most stoppages are usually in the horizontal section of the drain. If the lower floor units are backing-up then your problem will mostly be in the building drain (horizontal drain) under the slab. If this is the case, running the cable from the lowest unit will be the way to go.

__________________
IFIXH20 is offline  
 
Reply With Quote Quick reply to this message
Old 04-01-2014, 04:56 PM   #6
bobv
Junior Member
 
Join Date: Apr 2014
Posts: 3
Likes Given: 1

Default

Thanks, all. Do people think there's even value in preventative snaking of each unit? Someone else mentioned that it's not helpful/worth the cost (being charged $90 per unit) since it might actually contribute to a blockage since you can't usually run sufficient water to flush out whatever you dislodge. Does anyone else have an opinion on if hydro jetting the vertical line (once every few years?) would be appropriate? That'd at least solve the problem of lacking water to flush out what's dislodged.

__________________
bobv is offline  
 
Reply With Quote Quick reply to this message
Old 04-01-2014, 05:02 PM   #7
johnjh2o
Senior Member
 
johnjh2o's Avatar
 
Join Date: Jul 2011
Location: Melbourne, Florida
Posts: 2,683
Liked 466 Times on 366 Posts
Likes Given: 335

Default

If it's not broken don't fix it.

__________________

John

johnjh2o is offline  
 
Reply With Quote Quick reply to this message
Old 04-01-2014, 11:53 PM   #8
Carl399
Junior Member
 
Join Date: Apr 2014
Posts: 13
Liked 2 Times on 1 Posts
Likes Given: 3

Default

I work maintenance in an 18 story apt bldg (218 apts). From experience, a 3/4" cable in a 1 1/4" line would be overkill. A 5/16 or 3/8 with a proper sized drop head would work much better. You should run your mains and take on the individual apts as they are needed.

__________________
Carl399 is offline  
2
People Like This 
Reply With Quote Quick reply to this message
Old 08-02-2014, 04:30 AM   #9
mcgervase
Superjet Sewer and Drain
 
Join Date: Aug 2014
Location: Temecula, Ca
Posts: 3
Default

Each horizontal kitchen line on each floor will have grease buildup. Each should be cabled as a preventative going into the main stack, vertical. The main stack should then be cabled. If you add 20 feet plus to the cable run from each kitchen sink c/o you will have cabled the main stack little by little as you go down to ground floor. Remember, that 3/8 inch snake is worthless in a horizontal 3 inch or larger pipe. you need to find the nearest large c/o and run a bigger snake for the turn at the bottom of the stack as it goes horizontal to the main tie in.

__________________
mcgervase is offline  
 
Reply With Quote Quick reply to this message
Old 08-02-2014, 05:44 AM   #10
journeyman
the professional
 
journeyman's Avatar
 
Join Date: Oct 2012
Location: san diego, california
Posts: 278
Liked 87 Times on 68 Posts
Likes Given: 87

Default

each unit is probably owned by individual people. he is trying to keep the common line clear and then it is up to the individual units to take care of the horizontals if this is not accurate bobv please tell me. i do alot of hoa work and plumbers will always come in and say the problem is in the common line so the owners of units dont have to pay the bill. by keeping the common line maintained now the charge will go to the homeowner/tenant



__________________
journeyman is offline  
 
Reply With Quote Quick reply to this message
Reply


Quick Reply
Message:
Options

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Back water valve? or snaking? ch00ver General Plumbing Help 4 03-19-2014 03:27 PM
apartment with no running water pete32 General Plumbing Help 6 01-08-2014 11:42 PM
Apartment kitchen sink drains into bathtub CatShaw54 Toilets and Sinks 2 09-02-2013 12:42 AM
Apartment project that I am working on phishfood Project Display 40 06-10-2012 03:03 AM
Snaking water lines? Greencreekproperties Pumps and Wells 1 06-28-2011 04:47 AM

Newest Threads

LATEST SPONSOR DEALS