    Hello,

    I have one boiler in my house that currently supplies heat to both my unit and the ground floor. The previous owner seems to have zone heating setup, but for some reason or another, has just the top unit call for heat and it automatically heats up the bottom unit. My tenant on the bottom unit says she doesn't get enough heat while my unit feels nice and warm. I'm curious why since she has adequate radiators setup on the ground floor.

    Is it the way the piping is set up? Is my boiler not up to snuff? I've attached photos of the piping and where one zone valve goes vs the other. I feel the pressure forces the heat up, therefore bypassing the turn where the first zone valve is, which heats the ground floor.

    https://photos.app.goo.gl/yPySWw2wTzKYxkWbA
    https://photos.app.goo.gl/ksfXCFWp1igP5gMx8
     
  2. Oct 14, 2019 #2

    frodo

    frodo

    frodo

    Just call me Macgyver Professional Supporting Member

    Joined:
    Sep 28, 2014
    Messages:
    7,658
    Likes Received:
    2,372
    Location:
    ,
    all see in your picture is one zone valve

    heat rises. the top floor is going to be warmer than the bottom
    a 2 story should have 2 zones upstairs and down stairs

    a rental, should have there own zone. i would be raising hell. with the landlord
     
  3. Oct 14, 2019 #3

    Levski87

    Levski87

    Levski87

    Member

    Joined:
    Oct 14, 2019
    Messages:
    9
    Likes Received:
    0
    Location:
    07307
    There are two taco valves as shown in the photo. What do you mean by there is only one zone?
     
  4. Oct 14, 2019 #4

    frodo

    frodo

    frodo

    Just call me Macgyver Professional Supporting Member

    Joined:
    Sep 28, 2014
    Messages:
    7,658
    Likes Received:
    2,372
    Location:
    ,
    My bad
    the image is not very good. I did not see the other

    ave you verified the zone valve is working?
     
  5. Oct 14, 2019 #5

    Diehard

    Diehard

    Diehard

    Well-Known Member

    Joined:
    Aug 19, 2017
    Messages:
    2,006
    Likes Received:
    343
    Location:
    North Reading, Mass.
    ???
    I see 2 zone valves.
    Doesn't the first floor have a thermostat?
    Take some pictures further out with circulator, etc.
    The info you show on the boiler does not show the heat output. Should see something on MBH.
     
  6. Oct 14, 2019 #6

    frodo

    frodo

    frodo

    Just call me Macgyver Professional Supporting Member

    Joined:
    Sep 28, 2014
    Messages:
    7,658
    Likes Received:
    2,372
    Location:
    ,
    zone valve should have a manual override slide switch
    slide it to open if closed

    verify low voltage at stat
    verify power to zone valve
    verify transformer is operable
     
  7. Oct 14, 2019 #7

    Levski87

    Levski87

    Levski87

    Member

    Joined:
    Oct 14, 2019
    Messages:
    9
    Likes Received:
    0
    Location:
    07307
    I will check on the manual override, but in terms of the piping setup, is this correct? It seems odd that one pipe is facing up with the zone valve while the other breaks off that main pipe and turns. Ironically, the one facing up is the one that gets more heat.
     
  8. Oct 14, 2019 #8

    Levski87

    Levski87

    Levski87

    Member

    Joined:
    Oct 14, 2019
    Messages:
    9
    Likes Received:
    0
    Location:
    07307
    Also to note, the boiler has a 100k btu input and 80k output. The top unit is 1100 square feet and the bottom is 800 square feet.
     
  9. Oct 14, 2019 #9

    frodo

    frodo

    frodo

    Just call me Macgyver Professional Supporting Member

    Joined:
    Sep 28, 2014
    Messages:
    7,658
    Likes Received:
    2,372
    Location:
    ,
    To be honest with you
    you picture is to close to be able to determine what goes where
    BACK OFF and take a picture of the whole piping arrangement thing

    do you know how to post to the site?
    click upload a file. on the bottom of this chat box
    choose file. click enter
    click full image
    cousin it.gif
    it is pretty simple
     
  10. Oct 14, 2019 #10

    Diehard

    Diehard

    Diehard

    Well-Known Member

    Joined:
    Aug 19, 2017
    Messages:
    2,006
    Likes Received:
    343
    Location:
    North Reading, Mass.
    I believe this statement requires further clarification.
    "The previous owner seems to have zone heating setup, but for some reason or another, has just the top unit call for heat and it automatically heats up the bottom unit."
    So it sounds like you have 2 zones being controlled by one thermostat.
    You didn't answer the previous question, "Doesn't the first floor have a thermostat?"

    Sounds like your problem goes beyond the possibility of one of the two solenoids malfunctioning.
    Without going into a lot of details as to why or why not the problem appears to be the lack of independent control of the two zones.


    If that's the case, you can just refer back to frodo's first comments in post #2 and ignore his first line.
     
    Last edited: Oct 14, 2019
  11. Oct 14, 2019 #11

    Levski87

    Levski87

    Levski87

    Member

    Joined:
    Oct 14, 2019
    Messages:
    9
    Likes Received:
    0
    Location:
    07307
    My question is geared more towards the piping setup for the zones. Let's say in a perfect world, my zones are setup properly and they are both open at the same time due to a cold winter day. In my current piping infrastructure, knowing that heat rises, is my piping flawed or is it set up properly since one zone breaks off that main pipe and has the turn vs the other one that goes straight up?
     
  12. Oct 14, 2019 #12

    Diehard

    Diehard

    Diehard

    Well-Known Member

    Joined:
    Aug 19, 2017
    Messages:
    2,006
    Likes Received:
    343
    Location:
    North Reading, Mass.
    Yes I did recognize that really was the gist of your question but until we got a clear picture of what the real setup was, it may not mean much.

    Actually, yes the hot water rises faster in a vertical pipe on gravity systems but you don't have a gravity system. A pumped system should favor the path of least resistance(pipe size, length, number of fittings, etc.) There are a lot of other factors that would make a big difference the two areas in question.
    So I take it there is no thermostat for the first floor. The fact that there are two zone valves would indicate that one reason for the change could have been trying to conserve energy by not allowing the tenant to get carried away with excessive high heat settings with windows open, etc.
    If you're concerned with that type of thing there are other ways to handle it.

    Let me just ask this one last time. Is there a thermostat on the first floor?
     
    Last edited: Oct 14, 2019
  13. Oct 14, 2019 #13

    Levski87

    Levski87

    Levski87

    Member

    Joined:
    Oct 14, 2019
    Messages:
    9
    Likes Received:
    0
    Location:
    07307
    Correct. In the current system, the thermostat sits on my floor, which is the first floor. This thermostat triggers the heat, which fills the first floor and the ground floor.

    Let me give some background. I recently purchased this home and what I noticed is that the previous owner had installed these zone valves (one to control the first unit and one to control the ground unit) and each one had their own thermostat. Over the course of time, I'm unsure of the reason, the previous owner decided to only keep the first floor thermostat and completely disconnect the ground floor one. He also, and this is my assumption, decided to open the ground floor zone valve to always be open and automatically get heat when the first floor unit called for it.

    Due to this setup, I have noticed that the piping for the first floor is much hotter than the ground floor (this is tested by touching each pipe before and after the zone valve connections). The tenant on the ground floor has also highlighted that they don't get enough heat in the winter.
     
  14. Oct 14, 2019 #14

    Diehard

    Diehard

    Diehard

    Well-Known Member

    Joined:
    Aug 19, 2017
    Messages:
    2,006
    Likes Received:
    343
    Location:
    North Reading, Mass.
    Well I'd say put a thermostat back in the ground floor. Or you'll never have both areas heated to the desired temperatures.
     
  15. Oct 14, 2019 #15

    frodo

    frodo

    frodo

    Just call me Macgyver Professional Supporting Member

    Joined:
    Sep 28, 2014
    Messages:
    7,658
    Likes Received:
    2,372
    Location:
    ,
    couple of issues
    one is the t stat for the bottom floor not being hooked up
    the second is the flow rate of the heating water
    has the system been maintained by a hvac company?
    has the hvac company balanced the the flow between the 2 zones?
    has a balance company balanced the system as a whole to achieve optimum heat transfer
    the heated water must slow down in order for the heat to radiate

    rule of thumb is 1.5--3.0 gpm [ a jumping off point] that changes due to a variety of factors
    each system is different.
    if your flow is more than 3gpm. you are not heating efficiently
     
  16. Oct 14, 2019 #16

    Levski87

    Levski87

    Levski87

    Member

    Joined:
    Oct 14, 2019
    Messages:
    9
    Likes Received:
    0
    Location:
    07307
    Great points. Any recommendations for a company in NJ frodo :)
     
  17. Oct 14, 2019 #17

    Diehard

    Diehard

    Diehard

    Well-Known Member

    Joined:
    Aug 19, 2017
    Messages:
    2,006
    Likes Received:
    343
    Location:
    North Reading, Mass.
    LOL
    I was not implying to put back the thermostat without hooking it up.:eek:

    Sorry just couldn't resist!

    But on a more serious note, never seeing a multi-zone system using zone valves, what do they use to balance the zones heating areas? Balancing valves?
     
  18. Oct 15, 2019 #18

    frodo

    frodo

    frodo

    Just call me Macgyver Professional Supporting Member

    Joined:
    Sep 28, 2014
    Messages:
    7,658
    Likes Received:
    2,372
    Location:
    ,
    circuit_setter_001.png you
    you can save a lot of money, by installing a full port ball valve with a tee on either side of it. with petes plugs
    in the tees
     
  19. Oct 15, 2019 #19

    frodo

    frodo

    frodo

    Just call me Macgyver Professional Supporting Member

    Joined:
    Sep 28, 2014
    Messages:
    7,658
    Likes Received:
    2,372
    Location:
    ,
    No Bro, I am WAYYYYYY south of you
    I googled NJ
    www.rangerair.net/
     
  20. Oct 15, 2019 #20

    Levski87

    Levski87

    Levski87

    Member

    Joined:
    Oct 14, 2019
    Messages:
    9
    Likes Received:
    0
    Location:
    07307
    Photos aren't great, nor is the diagram.

    The G represents the green item in one of my photos. The R is the red item. I believe the R is where my return line goes, which is highlighted by the dotted line.
     