WH vent through roof close to parapet wall

Discussion in 'Plumbing Building Code' started by Gh0st, Jan 11, 2019.

Help Support Plumbing Forums by donating:

  1. Jan 11, 2019 #1

    Gh0st

    Gh0st

    Gh0st

    New Member

    Joined:
    Aug 15, 2017
    Messages:
    4
    Likes Received:
    0
    Location:
    ,
    New Mexico. 20190110_181946.jpg I cant find the part of code that states the distance from parapet wall.i want to say its 3 feet but my problem is i have to be 10 feet from the air intake that puts me up against the parapet wall.
     
  2. Jan 11, 2019 #2

    frodo

    frodo

    frodo

    Just call me Macgyver Professional Supporting Member

    Joined:
    Sep 28, 2014
    Messages:
    7,400
    Likes Received:
    2,311
    Location:
    ,
    parapet.png

    looks like if you are closer than 10' / but no closer than 2'

    the top of vent has to be 2' above parapet

    The above is uniform mechanical code
    ..................
    below is the international mechanical code
    #2 shows.....If close to intake be 3' higher that intake


    whvent__i_mech_code.png
     
    Last edited: Jan 11, 2019