Water leak issue

Discussion in 'General Plumbing Help' started by Geekfather, Aug 28, 2018.

Help Support Plumbing Forums by donating:

  1. Sep 7, 2018 #21

    Mikey

    Mikey

    Mikey

    Well-Known Member Supporting Member

    Joined:
    Jul 16, 2018
    Messages:
    234
    Likes Received:
    37
    Location:
    Northwest Washington
    We had a similar problem in a house in FL; aggressive soil ate pinhole leaks in the unprotected copper buried under the slab. Re-plumbed the entire house overhead.
     
  2. Sep 7, 2018 #22

    Diehard

    Diehard

    Diehard

    Well-Known Member

    Joined:
    Aug 19, 2017
    Messages:
    1,397
    Likes Received:
    243
    Location:
    North Reading, Mass.
    I suppose it's possible for the hot to go into he cold when the cold water is used at a Hot/Cold faucet if the cold water pressure drops. But I'm not too sure it would drop lower than the hot water side.
    Still no answer on whether it may be coming out the TPR valve. It's possible Geekfather didn't know what a temperature/pressure relief valve(TPR) is.
     
  3. Sep 7, 2018 #23

    Mikey

    Mikey

    Mikey

    Well-Known Member Supporting Member

    Joined:
    Jul 16, 2018
    Messages:
    234
    Likes Received:
    37
    Location:
    Northwest Washington
    It's called a "plumbing crossover". Many articles about it on the Web, looks like a common problem in commercial settings. I had heard about it in residential use, but never experienced it personally.
     
  4. Sep 7, 2018 #24

    Diehard

    Diehard

    Diehard

    Well-Known Member

    Joined:
    Aug 19, 2017
    Messages:
    1,397
    Likes Received:
    243
    Location:
    North Reading, Mass.
    Yes I do recall many of the commercial service sink faucets came with integral check valves. I suppose they were there for a reason.
     
  5. Sep 7, 2018 #25

    TomFOhio

    TomFOhio

    TomFOhio

    Professional Professional

    Joined:
    Jan 20, 2018
    Messages:
    822
    Likes Received:
    186
    Location:
    Mansfield,, Ohio
    I don't think its going to mix water unless the valve is turned on. He has hot water running someplace with all the
    faucets turned off and nothing leaking that he can see. He never did say whether he has any pipes going underground.
     
  6. Sep 8, 2018 #26

    Mikey

    Mikey

    Mikey

    Well-Known Member Supporting Member

    Joined:
    Jul 16, 2018
    Messages:
    234
    Likes Received:
    37
    Location:
    Northwest Washington
    As a last resort, he could call Sleuth.
     
  7. Sep 8, 2018 #27

    FishScreener

    FishScreener

    FishScreener

    Well-Known Member

    Joined:
    Aug 23, 2018
    Messages:
    258
    Likes Received:
    71
    Location:
    83467
    All too possible with single handle units, which now days is the tub/shower, lavatory and kitchen sinks. The seats wear and let water pass from one side to the other, without leaking out the tap.

    But, I’m still guessing the tpv is weeping, and outlet from the discharge the line is hidden.
     
    Mikey likes this.
  8. Sep 8, 2018 #28

    frodo

    frodo

    frodo

    Just call me Macgyver Professional Supporting Member

    Joined:
    Sep 28, 2014
    Messages:
    7,400
    Likes Received:
    2,312
    Location:
    ,
    Geekfather

    Please answer this question

    is the relief valve on the water heater leaking water out of the end of the pipe that is attached to the relief valve?
     
  9. Sep 8, 2018 #29

    Mikey

    Mikey

    Mikey

    Well-Known Member Supporting Member

    Joined:
    Jul 16, 2018
    Messages:
    234
    Likes Received:
    37
    Location:
    Northwest Washington
  10. Sep 8, 2018 #30

    frodo

    frodo

    frodo

    Just call me Macgyver Professional Supporting Member

    Joined:
    Sep 28, 2014
    Messages:
    7,400
    Likes Received:
    2,312
    Location:
    ,
    O the irony... there was a discussion recently on the forum about whether or not the TPR air gap had to a) exist, and/or b) be easy to see at the water heater.
    https://www.plumbingforums.com/threads/hot-water-draining-out-of-outside-drain.13433/#post-101273[/QUOTE]

    A air gap is required, It is required where the pipe indirectly connects with the sewer
    It is not required or allowed to be installed any where else,
    Back in the day, we used to pipe the pop off straight down to the WH pan, that was outlawed
    due to someone getting burned
     
    GReynolds929 likes this.
  11. Sep 9, 2018 #31

    Diehard

    Diehard

    Diehard

    Well-Known Member

    Joined:
    Aug 19, 2017
    Messages:
    1,397
    Likes Received:
    243
    Location:
    North Reading, Mass.
    Regarding the termination of water heaters TPR

    It's all up to how the local inspector interprets it.

    The intent of the requirement, however it may be worded, is that the possibility of back siphonage of a hazardous material is prevented.
     
  12. Sep 9, 2018 #32

    frodo

    frodo

    frodo

    Just call me Macgyver Professional Supporting Member

    Joined:
    Sep 28, 2014
    Messages:
    7,400
    Likes Received:
    2,312
    Location:
    ,
    608.5 Discharge Piping,

    The discharge piping serving a temperature relief valve, pressure relief valve, or combination of both shall have no valves, obstructions, or means of isolation and be provided with the following:

    (1) Equal to the size of the valve outlet and shall discharge full size to the flood level of the area

    receiving the discharge and pointing down.

    (2) Materials shall be rated at not less than the operating temperature of the system and

    approved for such use.

    (3) Discharge pipe shall discharge independently by gravity through an air gap into the drainage

    system or outside of the building with the end of the pipe not exceeding 2 feet (610 mm) and not less than 6 inches (152 mm) above the ground and pointing downwards.

    (4) Discharge in such a manner that does not cause personal injury or structural damage.

    (5) No part of such discharge pipe shall be trapped or subject to freezing.

    (6) The terminal end of the pipe shall not be threaded.

    (7) Discharge from a relief valve into a water heater pan shall be prohibited.

    Their is no alternative interpretation a T&P drain connects to the T&P with a male adaptor and the piping is run to a floor drain or floor sink with an air gap at the drain.
    OR it can run out the building and drain on the ground,
    it can not drain into the pan, nor tie into the pan drain,
     
    Last edited: Sep 9, 2018
  13. Sep 9, 2018 #33

    FishScreener

    FishScreener

    FishScreener

    Well-Known Member

    Joined:
    Aug 23, 2018
    Messages:
    258
    Likes Received:
    71
    Location:
    83467
    The plumbing section of the International Residential Code, adds that the discharge should located so as to be visible to residents so they can detect leaks.

    On my housing units I’ve started having a two inch drain line immediately below the tpv discharge line, the two inch runs through a trap filled with mineral oil to the main stack.
     
  14. Sep 9, 2018 #34

    TomFOhio

    TomFOhio

    TomFOhio

    Professional Professional

    Joined:
    Jan 20, 2018
    Messages:
    822
    Likes Received:
    186
    Location:
    Mansfield,, Ohio
    Looks like were more worried about this man's leak than he is. Where's he at????? Has any of these suggestions helped???
     
    Diehard likes this.
  15. Sep 10, 2018 #35

    Diehard

    Diehard

    Diehard

    Well-Known Member

    Joined:
    Aug 19, 2017
    Messages:
    1,397
    Likes Received:
    243
    Location:
    North Reading, Mass.
    Not to belabor the point, but if you look back at the link you provided in post #30 above, I believe you and Mikey had some differences in interpretation. (Post 12 through 15):D

    I'm not disagreeing with what you just posted in the 4 lines of text above. Just the part about, There is no alternative interpretation.
     
  16. Sep 10, 2018 #36

    Mikey

    Mikey

    Mikey

    Well-Known Member Supporting Member

    Joined:
    Jul 16, 2018
    Messages:
    234
    Likes Received:
    37
    Location:
    Northwest Washington
    @Diehard: I think you believe correctly. The neat thing about most codes is there is always an alternative interpretation. The only interpretation that always works is "when in doubt, ask your AHJ." I'll bet, however, that you could find AHJs around the country who would agree with Frodo, or me, or both, or neither.
     
    Diehard likes this.
  17. Sep 10, 2018 #37

    Mikey

    Mikey

    Mikey

    Well-Known Member Supporting Member

    Joined:
    Jul 16, 2018
    Messages:
    234
    Likes Received:
    37
    Location:
    Northwest Washington
    And, back on topic, I coincidentally have a hot-water-leaking-into-cold-side issue going on right now. Haven't investigated it yet, but it follows some re-plumbing of two bathrooms completed last week by professional plumbers.
     
  18. Sep 10, 2018 #38

    Diehard

    Diehard

    Diehard

    Well-Known Member

    Joined:
    Aug 19, 2017
    Messages:
    1,397
    Likes Received:
    243
    Location:
    North Reading, Mass.
    I've dealt with many inspectors over the years, regarding plumbing and cross connections control, in many different states around the country. In one case I had to send the guy back to his boss, he was so far off in his ideas.:rolleyes:
     
  19. Sep 10, 2018 #39

    Richard Gavle

    Richard Gavle

    Richard Gavle

    Well-Known Member

    Joined:
    Jun 4, 2018
    Messages:
    50
    Likes Received:
    10
    I have seen a few furnace humidifiers plumbed to hot water.
     
  20. Sep 10, 2018 #40

    Mikey

    Mikey

    Mikey

    Well-Known Member Supporting Member

    Joined:
    Jul 16, 2018
    Messages:
    234
    Likes Received:
    37
    Location:
    Northwest Washington
    Don't know if it's code or not, but it doesn't make much sense, unless there's provision for making sure the "hot water" is in fact hot at the time of use.
     