Vent/Drain help

Discussion in 'General Plumbing Help' started by staj, Nov 18, 2011.

Help Support Plumbing Forums by donating using the link above.
  1. Nov 18, 2011 #1

    staj

    staj

    staj

    New Member

    Joined:
    Nov 18, 2011
    Messages:
    4
    Likes Received:
    0
    Location:
    ,
    I'm replacing the iron drain with PVC and rearranging a few things.

    Can you provide some feedback on the attached two diagrams. My concern is the long horizontal vent run and the sink drain that wraps around and enters low. How do these look? Thank you for any input, appreciated.

    elevation.jpg

    elevation2.jpg
     
  2. Nov 18, 2011 #2

    johnjh2o

    johnjh2o

    johnjh2o

    Senior Member Professional

    Joined:
    Jul 21, 2011
    Messages:
    3,209
    Likes Received:
    733
    Location:
    Melbourne, Florida
    You can not have a horizontal below the flood rim of the highest fixture. Which in most cases is 42".

    John
     
  3. Nov 18, 2011 #3

    staj

    staj

    staj

    New Member

    Joined:
    Nov 18, 2011
    Messages:
    4
    Likes Received:
    0
    Location:
    ,
    Thanks John-
    Interesting, I heard that once before but just happened to forget it.

    What I find perplexing, however, is that if I was to move the Water Closet to the left in the diagram all the way to the stack essentially, this would take care of the "horizontal vent" problem. For that reason, I don't get it.

    I'm starting to think that I need a new stack in the house. Unfortunately, if I put it right above the sewer main, the stack would come out on the roof about 3.5 feet horizontally from a window and probably 3-5 feet below the highest point on the roof line (which I think violates UPC).

    Any thoughts or advice would be appreciated.

    Thanks again,
    Greg
     
  4. Nov 18, 2011 #4

    staj

    staj

    staj

    New Member

    Joined:
    Nov 18, 2011
    Messages:
    4
    Likes Received:
    0
    Location:
    ,
    I should have said, "...,I think this would take care of the "horizontal vent" problem because that is how the existing set up is."
     
  5. Nov 19, 2011 #5

    staj

    staj

    staj

    New Member

    Joined:
    Nov 18, 2011
    Messages:
    4
    Likes Received:
    0
    Location:
    ,
    How does this look? Is the stack that is at about a 45 degree angle in the attic o.k.?
    Thanks for the help.
    Greg

    diagram.jpg
     
  6. Nov 19, 2011 #6

    johnjh2o

    johnjh2o

    johnjh2o

    Senior Member Professional

    Joined:
    Jul 21, 2011
    Messages:
    3,209
    Likes Received:
    733
    Location:
    Melbourne, Florida
    Your not quite there. You can't have a waste line connecting in between a toilet and it's vent. Connect the shower to the same line that serves the sink below the floor just be sure to increase the line to 2".