Termination of water heater TP relief line

Help Support Plumbing Forums:

Copymutt

Member
Joined
Dec 2, 2019
Messages
21
Reaction score
6
Location
Durango,Co
Just installed a timer on this 6 gal. elec. water heater. Desiring to comply w/ code for termination of the PT relief pipe. Code says no more than 6” above or below structural floor. Other heaters in the home are terminated to outside structure 6” above ground because it was convenient. Since this is rework, that’s not very convenient.
Your suggestions please. Note the shop sink is right there, very convenient.
C7404FD6-7810-4329-B002-081A27883E2E.jpegC7404FD6-7810-4329-B002-081A27883E2E.jpeg
 

frodo

Just call me Macgyver
Professional
Supporting Member
Joined
Sep 28, 2014
Messages
8,000
Reaction score
2,516
Location
right here right now, over there later on.
1] your relief valve
Discharge in a manner that does not cause personal injury
Code requires it to discharge through a ''air gap'' that means the bottom of the pipe shall be 1'' above the rim of that sink.



2]water_heater_bottom_fed.png

1584551848930.png
 
Last edited:

SHEPLMBR

not a Junior Member anymore!
Sponsor
Joined
Mar 9, 2016
Messages
847
Reaction score
169
Location
NOKESVILLE, VA
1] your relief valve
Discharge in a manner that does not cause personal injury
Code requires it to discharge through a ''air gap'' that means the bottom of the pipe shall be 1'' above the rim of that sink.



2]View attachment 23787

View attachment 23788
ha! I have seen them (albeit not code) discharging into a non-used water fountain.
 

frodo

Just call me Macgyver
Professional
Supporting Member
Joined
Sep 28, 2014
Messages
8,000
Reaction score
2,516
Location
right here right now, over there later on.
Please explain the function of the vacuum relief valve. Thanks.
Vacuum Relief Valve
Featured snippet from the web
Vacuum relief valves are used in water heater/tank applications to automatically allow air to enter into the piping system to prevent vacuum conditions that could siphon the water from the system and damage water heater/tank equipment.



This is how I would pipe your WH
 

Attachments

Copymutt

Member
Joined
Dec 2, 2019
Messages
21
Reaction score
6
Location
Durango,Co
Thanks for all the input guys. I can’t perceive a vac relief needed unless there was a potential for siphoning via the PR termination, which I don’t intend to create. Terminating 1” above the sink would look like crap and interfere w/ the use of said sink, besides being a potential burn hazard. Other than just terminating inside above the floor, I see my only other option as running it down the inside wall and then outside to dump. There is no way you would not realize the PR valve has opened, however I’ve observed some pretty clueless people.
 
Last edited: