Maine-Islander
New Member
I have 5 year old dual float pump in my effluent tank and am getting an intermittent high water alarm. Sometimes the primary float will kick in normally on automatic and it will work fine for a few days. Other times the primary float doesn’t kick in and the high water alarm goes off and the pump immediately starts working. Still other times the high water will go off and the pump doesn’t kick in and I have to manually pump it. The control panel is a 2004 CSI controls panel that seems pretty basic. I’ve tested the primary pump float with an ohm meter and it works fine. Floats move freely. I’ve taken apart the contactor and all contacts are clean with no corrosion (the control box is in the house). I’ve even taken the switch apart and cleaned the contacts. All wires that should have 110 volts are getting 110. The only thing left to look at is a small relay that is powered by the high water float. It looks clean and seems to operate although I really can’t tell. I’ve ordered a new relay on the off chance that this is causing the problem.
Have any of you experienced this before?
Have any of you experienced this before?