    What is standard practice at the rough-in stage for PVC DWV piping that penetrates a slab floor? In particular, how are vents and drains terminated in (or above or below) the slab before the concrete work is done?

    Are all drains/vents brought through the slab and left projecting above the level of the concrete, a foot or so? (Presumably toilet drains are then cut off to finished floor level.) Or is there some standard practice that leaves the piping at or below concrete level at rough-in, and then the piping is extended through the slab after the concrete work and structural framing are completed?

    I'm an amateur with some experience with under-slab DWV plumbing but in the past have used what must be non-standard approaches to this question. (I believe I'm adequately informed/experienced with pipe sizing and pipe layouts including under-slab practices, and can satisfy local building codes.)
     
  2. Mar 1, 2011 #2

    phishfood

    phishfood

    phishfood

    Well-Known Member Supporting Member

    Joined:
    Jan 18, 2010
    Messages:
    5,683
    Likes Received:
    965
    Location:
    Orlando, FL
    Water closets a few inches above the concrete, sink, lavatory, and laundry drains and vents ~24" above. The only time I terminate flush with concrete is in types of construction that utilize rollout forms for pouring upper floors.

    Under slab rough-in can seem deceptively simple, but it is really easy to screw up. And with layoffs rampant in building departments as local governments try to balance their budgets, don't count on the inspector to catch every issue. If you have a question, do not hesitate to ask us.
     
  3. Mar 1, 2011 #3

    PrecisionPlumbing

    PrecisionPlumbing

    PrecisionPlumbing

    Master Plumber Professional

    Joined:
    Feb 17, 2011
    Messages:
    17
    Likes Received:
    0
    Location:
    Dallas, Texas
    all piping needs to be sleeved in plasic where concrete will touch and stubbed 24" above the floor
     