Hot water heater luke warm

Discussion in 'Water Heaters and Softeners' started by wolfwolf, Aug 7, 2016.

Help Support Plumbing Forums by donating:

  1. Aug 7, 2016 #1

    wolfwolf

    wolfwolf

    wolfwolf

    Member

    Joined:
    Aug 7, 2016
    Messages:
    6
    Likes Received:
    0
    Location:
    ,
    So about 6 days ago our hot water heater started producing luke warm water.
    1. We checked the elements 1 was bad and replaced them both
    2. We by passed the thermostats to auto power the bottom element (We got hot water)
    3. Knowing we most likely blew the elements we replaced them both AGAIN
    4. We thought the thermostat was bad replaced them both
    5. We than checked every single wire no issue 240v everything its testing 100% fine
    6. We did find out the breaker was somewhat burnt and replaced the breaker
    7. After wiring it back up right, back to luke warm water
    Decide to replace the water heater and buy a brand new one.

    Put it in installed.
    1. Turned all of the faucets on to make sure it properly filled up
    2. Made sure the heater was 100% full
    3. Turned the power back on
    4. Waited 2hrs got luke warm water again
    5. (decide) to wait 6hrs still luke warm water

    We cant really think of ANYTHING wrong to make the heater not heat right...
    (We use will water, it is summer so the water didn't suddenly drop in temp. either)
     
    Last edited: Aug 7, 2016
  2. Aug 7, 2016 #2

    frodo

    frodo

    frodo

    Just call me Macgyver Professional Supporting Member

    Joined:
    Sep 28, 2014
    Messages:
    7,658
    Likes Received:
    2,372
    Location:
    ,
    double check upper/lower element is correct element for heater

    look at both t-stats set at 110 degrees

    check your electrical connections for tightness

    check braker for tripped condition
     
  3. Aug 7, 2016 #3

    phishfood

    phishfood

    phishfood

    Moderator Staff Member Professional Supporting Member

    Joined:
    Jan 18, 2010
    Messages:
    5,775
    Likes Received:
    992
    Location:
    Orlando, FL
    Use a pan to catch some water from the relief valve, and use a kitchen thermometer to check the temperature of that.
     
  4. Aug 7, 2016 #4

    journeyman

    journeyman

    journeyman

    the professional

    Joined:
    Oct 4, 2012
    Messages:
    538
    Likes Received:
    165
    Location:
    san diego, california
    It is possible you have a bad dip tube on heater
     
  5. Aug 7, 2016 #5

    wolfwolf

    wolfwolf

    wolfwolf

    Member

    Joined:
    Aug 7, 2016
    Messages:
    6
    Likes Received:
    0
    Location:
    ,
    @frodo It is because it came from the factory, Both were set all the way to 90, connections 100% tight, Breaker is 100% perfect
    @journeyman Our old water heater was doing the same exact thing (Both dip tubes are perfect)

    We decide to disconnect the bottom element to see if the top one would heat.
    Once we did that the water went from 70degrees up too 90 degrees now from the tap
    We turned the bottom thermostat up too 120 and awaiting results (Before the bottom element would never turn on so were getting somewhere)
     
    Last edited: Aug 7, 2016
  6. Aug 8, 2016 #6

    journeyman

    journeyman

    journeyman

    the professional

    Joined:
    Oct 4, 2012
    Messages:
    538
    Likes Received:
    165
    Location:
    san diego, california
    Ok let me ask did you completely fill tank with water before start up if not it will burn out elements
     
  7. Aug 8, 2016 #7

    johnjh2o

    johnjh2o

    johnjh2o

    Senior Member Professional Lifetime Supporter

    Joined:
    Jul 21, 2011
    Messages:
    3,275
    Likes Received:
    746
    Location:
    Melbourne, Florida
    Could be a faulty cartridge in a tub or shower single lever valve causing the cold water to mix with the hot though out the system.
     
    journeyman and SHR like this.
  8. Aug 8, 2016 #8

    wolfwolf

    wolfwolf

    wolfwolf

    Member

    Joined:
    Aug 7, 2016
    Messages:
    6
    Likes Received:
    0
    Location:
    ,
    @journeyman yes after 5hrs the tank better be full when we replaced the 2 elements AGAIN today
    @johnjh2o weve checked theres not mixing between hot and cold water anywhere

    Water is still only luke warm
     
  9. Aug 8, 2016 #9

    journeyman

    journeyman

    journeyman

    the professional

    Joined:
    Oct 4, 2012
    Messages:
    538
    Likes Received:
    165
    Location:
    san diego, california
    Turn off hot water valve to house then go to faucet and turn on hot side if water comes out you have a bleed over
     
  10. Aug 8, 2016 #10

    wolfwolf

    wolfwolf

    wolfwolf

    Member

    Joined:
    Aug 7, 2016
    Messages:
    6
    Likes Received:
    0
    Location:
    ,
    0 bleed over
     
  11. Aug 8, 2016 #11

    Caduceus

    Caduceus

    Caduceus

    Professional Professional

    Joined:
    Apr 3, 2011
    Messages:
    1,288
    Likes Received:
    353
    Location:
    Pittsburgh, PA
    Did you check the water temperature from the T&P valve as phishfood recommended? for two tanks to suddenly have the same issue, especially the new one, there has to be something being missed here. Has anything been worked on or added to the plumbing recently? It does sound like a cross over of hot and cold. When checking for cross over, did you check from a two handled faucet?
     
    phishfood likes this.
  12. Aug 8, 2016 #12

    wolfwolf

    wolfwolf

    wolfwolf

    Member

    Joined:
    Aug 7, 2016
    Messages:
    6
    Likes Received:
    0
    Location:
    ,
    @caduceus No plumbing work has been done for over 2years, yes we checked from all of the faucets in the hose shower and all there is 0 cross over

    Home depot told us to bring it back and get a brand new one, they said if it dosnt work there going to send over there person who manages there plumbers for this area to look at it
     
  13. Aug 8, 2016 #13

    frodo

    frodo

    frodo

    Just call me Macgyver Professional Supporting Member

    Joined:
    Sep 28, 2014
    Messages:
    7,658
    Likes Received:
    2,372
    Location:
    ,
    when you filled the water heater with water, did you bleed the air out of the tank as it was filling ?

    before you turned on the element?

    what faucet did you use to bleeed the air ?

    my guess is the faucet has trash in the divertor from bleeding causeing it to bleed over
     
  14. Aug 9, 2016 #14

    wolfwolf

    wolfwolf

    wolfwolf

    Member

    Joined:
    Aug 7, 2016
    Messages:
    6
    Likes Received:
    0
    Location:
    ,
    Turn out it was a bad hot water heater, the new one works great :D! Thanks for all the help!
     
  15. Aug 11, 2016 #15

    LimitlessHsolutions

    LimitlessHsolutions

    LimitlessHsolutions

    Member

    Joined:
    Jun 23, 2016
    Messages:
    10
    Likes Received:
    2
    Location:
    Ontario, Canada
    Now I think buying the new one is the only option !!
     
  16. Aug 16, 2016 #16

    InnovativePP

    InnovativePP

    InnovativePP

    Las Vegas Plumber

    Joined:
    Aug 16, 2016
    Messages:
    1
    Likes Received:
    0
    Location:
    Henderson, Nevada
    Is there a recirculating pump on the unit? If so, it could be failing. If not, perhaps the anode rod needs to be replaced.

    I would have initially guessed that it was the heating element but since you replaced that already, it could be that there is sediment in the heater and flushing it could remove a majority of the deposits. Good luck!
     