Gas fire - thermopile issue? Pilot lights but no flame.

Help Support Plumbing Forums:

Twowaxhack

Professional
Professional
Joined
Feb 9, 2021
Messages
5,749
Reaction score
2,591
Location
United states
Dawn dish soap in a spray bottle with warm water makes a pretty good leak detector.

Don’t over tighten things thinking tighter is better, it’s not.

Don’t use Teflon on flare fittings.

Check all connections for tightness and being leak free. Twice.
 

Tim Whistler

Active Member
Joined
Jul 5, 2021
Messages
34
Reaction score
18
Location
Silver Spring, MD
What's your OUTLET (or 'manifold') pressure? 10.2 isn't very bad, it still ought to work.
You did remove and clear the burner orifice right?
 

Tim Whistler

Active Member
Joined
Jul 5, 2021
Messages
34
Reaction score
18
Location
Silver Spring, MD
At 10.2 inlet it should be working, that's close enough. it doesn't seem like a gas pressure issue to me. Did you try to test the outlet pressure while turning the burner on? That's when you're going to see if it's getting gas or not.
What was the thermocouple reading? If it was above 15mv then it's either a clogged orifice or a bad valve.
We work on gas fireplaces all the time here in Maryland this time of year. They are really pretty simple until you get into the higher end electronic ignition models -
 

hcanning

Well-Known Member
Joined
Sep 23, 2021
Messages
47
Reaction score
1
Location
Usa
Ok thanks. As an FYI isn't it bizarre the gas can satisfy all my stove burners as attached. Tricky one. I'll likely get my plumber to do the regulator stuff.
 

Attachments

hcanning

Well-Known Member
Joined
Sep 23, 2021
Messages
47
Reaction score
1
Location
Usa
What's your OUTLET (or 'manifold') pressure? 10.2 isn't very bad, it still ought to work.
You did remove and clear the burner orifice right?
Thanks. Yes I cleaned out that orifice and Every single tube. Tightened every fitting
 

hcanning

Well-Known Member
Joined
Sep 23, 2021
Messages
47
Reaction score
1
Location
Usa
At 10.2 inlet it should be working, that's close enough. it doesn't seem like a gas pressure issue to me. Did you try to test the outlet pressure while turning the burner on? That's when you're going to see if it's getting gas or not.
What was the thermocouple reading? If it was above 15mv then it's either a clogged orifice or a bad valve.
We work on gas fireplaces all the time here in Maryland this time of year. They are really pretty simple until you get into the higher end electronic ignition models -
I'm a DIYer who knows nothing about the voltage side of things. I did however replace the thermocouple assembly with a new one but same issue. Pilot lights but burner won't flame up. Thanks. I'm just afraid of buying another fireplace and it not working.
 

hcanning

Well-Known Member
Joined
Sep 23, 2021
Messages
47
Reaction score
1
Location
Usa
Propane Technician came and checked the regulator hardware and boosted the gas inlet pressure to 11.25WC from 10.2WC at the gas fireplace inlet port. Fireplace still doesn't flame up so it must be a crappy valve coincidentally breaking the day the gas stove was installed. Go figure. Anyway. The End.
Anyone know where to get a budget refurb replacement valve or refurb gas fireplace Ma direction that I can switch this out with easily?
Thanks all for your help.
 

tailgunner

Member
Joined
Aug 18, 2014
Messages
24
Reaction score
3
Location
,
Does your fireplace have both a thermocuple and thermopile ? If your pilot light is working, its not the thermocuple.
 

hcanning

Well-Known Member
Joined
Sep 23, 2021
Messages
47
Reaction score
1
Location
Usa
Does your fireplace have both a thermocuple and thermopile ? If your pilot light is working, its not the thermocuple.
It only has a thermocouple according to the manufacturer support guy. Thanks
 