Hi:

I am changing my 2nd story tub from a LH to RH drain, so you don't have climb in between the toilet and the tub to turn on the shower. I'm in PA so I believe that I need to play by IPC rules. Originally all the plumbing was along one wall with lav, toilet and tub in a row. When I opened the walls, I was expecting to see vent stacks for all 3 fixtures, as shown below, but there is only the one behind the toilet. The distance from the tub drain to the stack is 3 feet in the current configuration. Tub drain is 1 1/2" PVC. If I move the tub drain to a RH configuration (adding 5 ft.), am I out of spec? And more importantly, any concerns about doing it even if it meets code? I can get a vent up to the attic without too much trouble if need be.

BTW, I was expecting to see venting as shown in the diagram but the only vent is behind the toilet. I have the walls open behind the lav and the tub and no vents are present. Out of curiosity, does the as built configuration meet code requirements? Thanks in advance Expected Venting With Text.png
 
If you flipped the tub without adding a vent, you would exceed the allowable developed length for 1.5” pipe.
You would have to put so much fall on the pipe it would become the form of an S-trap, that would be illegal.

Your current configuration meets code.

You could add a vent and flip the tub.

This would be a good place for an AAV if your inspector would allow it, if not then add a vent through the roof or revert into an existing vent in the attic.
 