city correction; help needed

Discussion in 'Plumbing Building Code' started by Tamas, Oct 6, 2018.

Help Support Plumbing Forums by donating using the link above.
  1. Oct 6, 2018 #1

    Tamas

    Tamas

    Tamas

    Well-Known Member

    Joined:
    Aug 29, 2014
    Messages:
    53
    Likes Received:
    0
    Location:
    ,
    Hi,
    Can you help me with this corrections from Glendale, CA city
    I can not understand well
    Thank you
     

    Attached Files:

  2. Oct 6, 2018 #2

    havasu

    havasu

    havasu

    Administrator Staff Member Admin

    Joined:
    Jan 6, 2010
    Messages:
    9,124
    Likes Received:
    1,238
    Location:
    Southern California,
    Can you type out those two sentences? Many folks here are leery of opening up unknown PDF's.
     
  3. Oct 6, 2018 #3

    RenewDave

    RenewDave

    RenewDave

    Well-Known Member

    Joined:
    Feb 18, 2018
    Messages:
    82
    Likes Received:
    11
    Location:
    ,
    What don’t you understand? Pretty straight forward corrections.
     
  4. Oct 10, 2018 at 8:13 PM #4

    Diehard

    Diehard

    Diehard

    Well-Known Member

    Joined:
    Aug 19, 2017
    Messages:
    331
    Likes Received:
    78
    Location:
    North reading, Mass.
    Here are the comments...
    Glendale CA Plumbing comments.jpg
    That first comment very similar to another commenters question. Don't think that got cleared up.(I think it was a different person.???)
     
  5. Oct 10, 2018 at 8:15 PM #5

    Diehard

    Diehard

    Diehard

    Well-Known Member

    Joined:
    Aug 19, 2017
    Messages:
    331
    Likes Received:
    78
    Location:
    North reading, Mass.
    What exactly is that first comment saying, exactly. I can make some assumptions.
     
  6. Oct 10, 2018 at 9:31 PM #6

    Jamesplumbing06

    Jamesplumbing06

    Jamesplumbing06

    Well-Known Member

    Joined:
    Feb 24, 2016
    Messages:
    237
    Likes Received:
    44
    Location:
    ,
    If you have 3” pipe use 3” cleanout. Now go to street connection. Measure back 5’. Install cleaniut more than 5’ from main.
    The 2@ arm over says 5’ so don’t arm over more than 5’ to turn your elbow out of wall. May have to move the vertical vent over toward sink.
     
  7. Oct 11, 2018 at 12:51 AM #7

    Diehard

    Diehard

    Diehard

    Well-Known Member

    Joined:
    Aug 19, 2017
    Messages:
    331
    Likes Received:
    78
    Location:
    North reading, Mass.
    So that's saying you must have an exterior cleanout when the main is over 5' from house???:eek: I must be missing something here. I've never heard of such a thing. I'm assuming the main is in the street.
    Or is the street connection within the house. I just can't get it to make any sense to me.

    I know I must be embarrassing myself here.:(
     
  8. Oct 11, 2018 at 12:54 AM #8

    FishScreener

    FishScreener

    FishScreener

    Well-Known Member

    Joined:
    Aug 23, 2018
    Messages:
    117
    Likes Received:
    33
    Location:
    83467
    You need a clean out at the uphill end of all waste lines that run more than five feet from the main.
     
    breplum likes this.
  9. Oct 11, 2018 at 1:36 AM #9

    Diehard

    Diehard

    Diehard

    Well-Known Member

    Joined:
    Aug 19, 2017
    Messages:
    331
    Likes Received:
    78
    Location:
    North reading, Mass.
    Well thanks for your patience. I guess I understand what you guys are saying now. I just never realized that was a requirement.
    I wonder if has anything to do with the fact that the building drain, and I believe the plumbers jurisdiction, in Massachusetts, terminates at a point ten feet outside the inner surface of a building’s foundation wall.
    I'll have to check with some of the locals.
     
  10. Oct 11, 2018 at 3:39 AM #10

    FishScreener

    FishScreener

    FishScreener

    Well-Known Member

    Joined:
    Aug 23, 2018
    Messages:
    117
    Likes Received:
    33
    Location:
    83467
    That’s another local code variation that is common. When I was in Nevada, a plumber could only work from the water meter forward on water, and from the property line in for sewer. It took a license as an underground piping contractor, to go from the mains to the property line, and set the meter, but that contractor couldn’t work on the plumbing side of the line. Snaking to the main was a kind of grey area, that the Contractor’s Board resolved by saying a plumber can snake to the sewer main.
     
    Diehard likes this.
  11. Oct 11, 2018 at 11:52 AM #11

    Jamesplumbing06

    Jamesplumbing06

    Jamesplumbing06

    Well-Known Member

    Joined:
    Feb 24, 2016
    Messages:
    237
    Likes Received:
    44
    Location:
    ,
    The “ main “ they are talking about. I believe to be sewer or septic. . Your house better be 5’ from sewer. Here we are required to have a cleanout as the building drain exits building on the exterior. Then if necessary every 65’ but no closer than 10’ from main.
    I don’t know how to bring someone else in but diehard and Frodo can draw on their posts and make a diagram. I figured one of them would have done it already.
    That book that some of these guys sleep by and beat the snot out of daily. Yeah that book was written by burocrats. Political burocrats. So you have to think like a lawyer to understand the tricks. I hate that stupid book. By stupid book I mean the magical code book. I would make a horrible cop.
     
    Diehard likes this.
  12. Oct 12, 2018 at 1:53 PM #12

    FishScreener

    FishScreener

    FishScreener

    Well-Known Member

    Joined:
    Aug 23, 2018
    Messages:
    117
    Likes Received:
    33
    Location:
    83467
    The codes are free online. The Code with Commentary, isn’t. And having the Code with the Commentary, is worth the money.

    The commentary explains, why they included the requirement. The model codes are actually written by Engineers, Tradesmen, and Manufacturers. There is very little in the codes that don’t have real reasons for being there. And, the commentary explains what they are trying to accomplish.

    The local modifications, are frequently written by local politicians, and are almost always the things that are strange, and don’t make sense. Because many of them are purely political, and have no logical reason to be there.
     
  13. Oct 12, 2018 at 4:09 PM #13

    RenewDave

    RenewDave

    RenewDave

    Well-Known Member

    Joined:
    Feb 18, 2018
    Messages:
    82
    Likes Received:
    11
    Location:
    ,
    Sounds like you have a three inch drain under your house that has a branch that is more than 5 feet off the main. This line must have a CO on the end of that line. Easy Peasy.
     
    breplum likes this.
  14. Oct 12, 2018 at 4:47 PM #14

    Diehard

    Diehard

    Diehard

    Well-Known Member

    Joined:
    Aug 19, 2017
    Messages:
    331
    Likes Received:
    78
    Location:
    North reading, Mass.
    Does anyone have a drain branch from their house that is NOT more than 5 feet off the main?
    Also, there are plumbing codes that don't go beyond 5 to 10 feet from the foundation.
     
  15. Oct 13, 2018 at 3:37 AM #15

    RenewDave

    RenewDave

    RenewDave

    Well-Known Member

    Joined:
    Feb 18, 2018
    Messages:
    82
    Likes Received:
    11
    Location:
    ,
    It’s within the building. We lay out our “trunk” lines so that the branches are as close to the “trunk” as possible. Less than 5 feet, I save a combi and a clean out.
     
  16. Oct 14, 2018 at 6:19 AM #16

    frodo

    frodo

    frodo

    Just call me Macgyver Professional Supporting Member

    Joined:
    Sep 28, 2014
    Messages:
    6,304
    Likes Received:
    1,961
    Location:
    ,
    1] you have a 3'' pipe that is within 5' from the outside wall, he wants a clean out on that pipe

    2] you have a 2'' p trap, that is more than 5' from the vent,



    6.5x552.JPG
     

Share This Page