I think I managed to get it all in right....anything I missed here or need to change up next time?

not shown is the vent upstream of the shower.

1599921374379.jpeg

Thanks!!
 
Last edited by a moderator:

GReynolds929

Professional
Professional
Joined
Jun 16, 2018
Messages
31
Reaction score
12
Where's the vent? Wet venting is done thru a lav, tub, shower, or bidet vent. Is the lav drain by the toilet? Shower to the right? You'll need a 2" trap. The clean out in the middle of the floor is illegal unless there will be an access cover with 18" clearance in front of the clean out. Needs to be above floor and or accessible. Santees cannot be used horizontal, should be a combo, or 90. Where does the pipe on the right go to? I know there's a lot of questions here, but that's what jumped out at me.
 