I believe what it boils down to, as far as the type of device required, would be based on whether it is subject to Back Pressure or just Back Siphonage.
And that could be based on whether the discharges of each type pump are tied into each other or run independently and whether it meets with the approval of the public water system purveyor.
The following was taken from the Ohio Cross Control Regulations of 2015.
Water Operated Sump Pumps/Devices
Some devices use the pressure provided by the public water system to operate. For example, water-operated backup sump pumps for homes and businesses utilize water pressure through the venturi principle instead of electricity to power the movement of collected sump water to the building’s drains. Such a configuration creates a cross-connection between the potable public water supply and liquid of a questionable quality. Due consideration must be given to the level of protection that is necessary to mitigate the hazard associated with the cross-connection. If alternative means exist which do not utilize water pressure or public water supply to operate the unit, they should take priority.
Specifically for water-operated backup sump pumps the following shall be taken into consideration:
1. Water-operated sump pumps pose a potential backflow hazard by way of a cross-connection between the drinking water supply and the contaminated water in the sump pit. This hazard is increased during flooding conditions. The main sump pump offers a potential of imposing backpressure against the water supply line to the water-operated backup sump pump if the discharge lines are combined. A majority of these pumps provide a vacuum breaker device for protection against backsiphonage. A vacuum breaker device would not provide the level of protection necessary if a backpressure situation should occur and would be made obsolete if it became submerged during a flooding situation.
2. The public water system purveyor must analyze each household or building considering installation of a water-operated sump pump on an individual basis to determine if a backflow hazard has been mitigated.
3. In all situations in which a water-operated backup sump pump is installed, the main sump pump and the water-operated backup sump pump should have completely separate discharge piping. Separate discharge piping is necessary if the backflow preventer installed is not rated for backpressure.
4. The installation of water-operated backup sump pump units should also be coordinated with the local building department, local health department, or the Ohio Department of Commerce, Industrial Compliance Division which regulates larger residential and commercial plumbing applications. For installation in a non-residential building, one of these authorities will approve the plans and inspect the plumbing installation to ensure that proper backflow prevention is provided. For residential buildings, the proposed plumbing installation may be reviewed and inspected where a local certified building department or a local health department is available to enforce the plumbing code. Water-powered sump pumps are permitted in the Ohio Plumbing Code. At time of issuance, the relevant sections of the OPC include sections 608.3, 608.12, 608.16.6, and 1113.1.5 (Rules 4101:3-6-01 and 4101:3-11-01 of the Administrative Code).
Figure 44 provides a schematic of a type of water-operated backup sump pump.
Figure 44. Schematic of a water-operated backup sump pump installation which uses
potable water supply to facilitate suction of fluids from the sump pit to
discharge location if primary pump fails.