Adding a Kick Space Heater to Cast Iron Radiator Loop - Need Help

Plumbing Forums

Help Support Plumbing Forums:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

europe72dead

Well-Known Member
Joined
Apr 7, 2020
Messages
93
Reaction score
12
Location
New Jersey
I'm currently renovating my kitchen and need wall space where an old cast iron radiator was. I've already removed the cast iron radiator and capped the feed/return lines in preparation for the kick space heater I plan to add. Before I get started I want to outline my plan and ask a few questions. I'd love input of any kind.

I do know that my replacement kick space heater is inferior to my original cast iron radiator however the new kitchen design requires it. I also know that I should create a separate loop specifically for the kick space heaters as they will call for hot water more frequently than a cast iron radiator that continues emitting heat long after the boiler shuts off. Since my piping is in the basement I plan to add the kick space heater to the same loop as my radiators and if needed in the future, add a separate zone if things are wonky next winter. My current system is an old converted gravity fed system with 5 radiators on the first floor and 7 on the second floor (originally 7 on the first floor). The last piece of information before I begin- My kitchen originally had two cast iron radiators. One was replaced with a kick space heater in the 90s (photos below with monoflo tee loop) and the other one is what I'm adding a kick space heater to now. The finished room will have two kick space heaters. I'm planning to buy either (2) BM K84 or K120 Twin Flow heaters. I'll be replacing the original kick space heater at the same time as I add the second.

Question 1) Will having two kick space heaters in this loop effect other radiators? There was no difference in performance with the original KS heater in place this past winter. Should I keep my original kick space heater piping exactly as is? Now would be the time to change it if needed.

Question 2) Can I have pipe going from my main supply directly into the new/ additional kick space i plan to install and then return directly into the main return pipe or will I need a monoflo setup like in my original kick space heater.

Question 3) Do I need a low temp aquastat for my new kick space heater? I don't think the original kick space heater had one but I've already trashed it and can't be sure.

Question 4) Is there anything else I should be concerned about?

I plan to use copper or pex al pex and will be including a baseboard vent elbow on the return line so that I can bleed the unit. I will likely reduce down to 1/2" copper/pex directly from the 3/4" steel ball valve I've installed off the main and then run directly to the kick space unit.

1.jpg
2.jpg
3.jpg
 
Last edited:
You don't need monoflow tees if your piping off of the green lines. They used monoflow tees on the other because the supply and return are on the same pipe.

I don't like monoflow tees. But if you had no issues with the old heater and your new is the same you should be able to use the old piping for that one.
 
The run with the mono flow tees connects both main supply and main return. I’m just trying to understand why.
 
Connecting the main supply and return pipes where the original kick space is located.
 
I'm guessing the "original" heater was added. They hooked on wherever was easiest.
 
If the Supply and return are separate pipes that connect to the boiler supply and return and are both dead-ended on the far end, then monoflo tees are not used. If the supply and return is one big loop from the supply of the boiler to the return of the boiler, then monoflo tees are needed, and should be installed in pairs. Piping all of the radiators in series is a bad idea, especially for kick space heaters which only have 1/2" tubing.
BTW, the kick space heaters can also be mounted in a flush or surface mounted wall cabinet. They also always come with a strapped on aquastat in the heater, typically set at 120 degF.
 
I believe I have a two pipe direct return system similar to what’s illustrated below.

929B51DA-9A34-489E-A03B-61FF646E85C8.jpeg
 
Any thoughts as to why these supply and return mains are tied together where the original monoflow t loop was placed for the original kickspace heater?

I just don’t understand why this is setup this way.
 
So that the heater gets the water it needs and the rest bypasses it. I'm guessing if you figured out the flow rates, the heater wouldn't return enough water fast enough. If there was a radiator there originally it probably had larger piping attached to it, and could return the water at the appropriate rate.
 
This makes a lot of sense. Using this same methodology, I would setup my “new” kick space heater the same way my “original” kick space heater is piped by tieing both feed and return together and adding monoflows in-between?
 
Why not just tie onto the green piping that is ready and has valves. One is supply and one is return. It would be a lot easier.
 
I thought the monoflow loop was required with this setup? I agree it would be much easier just reduce down to 1/2” and run lines directly from the supply and return to the kickspace heater.

I guess may last question is why would the monoflow loop be required in my first kickspace but not my second one? I assume because my first was the end of the supply /return main run?

you had originally said - “They used monoflow tees on the other because the supply and return are on the same pipe.” I assume the original cast iron radiator was the thing that connected the supply and return closing the loop.
 
They aren't required.

The pressure drop from the kicks pace heater restricted the flow at the end of the main so they used monoflow tees. If you hook onto the other piping your no longer at the end of the main. Your before it and the tees are nowhere near each other.
 
You only need them when you have a one pipe pipe system. Look above in the picture you posted. There are no monoflow tees.
 
Great this is actually very simple, add feed and return lines directly from the mains into the kickspace.

additionally I’ll add a vent/ baseboard elbow on the return lines of both kicks so there’s a way to bleed. I’m planning to use something like this. I also assume the Pex needs to also have an oxygen barrier or Pex al Pex
 

Attachments

  • B1931E9E-5084-45C3-8CD2-ECC9D75659BC.jpeg
    B1931E9E-5084-45C3-8CD2-ECC9D75659BC.jpeg
    248.4 KB · Views: 0
Great I will go with hepex as opposed to pex al pex. I just assumed that having the aluminum oxygen barrier would be best but you don’t know unless you ask.... Really appreciate the assistance
 