UPC Trap to Vent Distance (TUB)

Plumbing Forums

Help Support Plumbing Forums:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

PlumbingSocal

Active Member
Joined
Apr 30, 2021
Messages
28
Reaction score
7
Location
Lake Arrowhead, CA
I’m trying to figure out the proper trap to vent distance on a tub for UPC. The code book is a bit confusing.

FOR 1.5” trap
FOR 2” trap

From what I understand IPC is 6’ for 1.5” and 8’ for 2” trap, not sure about UPC.
 
I always thought it was 2 and a half time the diameter. But I could be wrong. Or that might be the IPC. I could be wrong all together.
 
I did it from memory (in trade since 1975).
3" is 6' 0"
UPC Table 10-1 Horizontal Distance of Trap Arms (Except for water closets) (which is always 6' even for 4")
 