Pressure relief valve question

Plumbing Forums

Help Support Plumbing Forums:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.
Joined
Apr 5, 2021
Messages
8
Reaction score
0
Location
Tampa
I have PVC plumbing and an outside shower that connects to the hot and cold water lines from the house. There is a brass pressure relief valve that comes off of the shower. This pressure relief valve was dripping so I replaced it. The new one lasted for about 3 months and is dripping again. I don't know any other neighbors that have a pressure relief valve other than the one that is connected to the water heater. Do I actually need this or can I cap it off? I have noticed that if I turn on multiple showers inside the house on at the same time the pipes will occasionly knock. Not sure if that is related to this pressure relief valve or if this is causing more of a problem than a help. Any advice would be appreciated here it
 
Your relief valve is doing its job. You may have a way of heating that shower that is seperate from your water heater (heat exchanger) I'm guessing since you don't have a piping schematic, but you probably need an expansion tank to stop the relief valve from popping.
 
I had my house repiped about 4 years ago and I know that the only thing heating the showers is the hot water heater. If that's the case is this valve still needed since there's one on the hot water heater? This valve is a constant dripping all day long and I don't think it's supposed to be doing that.
 
The hot water is expanding. Is there a check valve somewhere? Prv? If your piping is cut off from the rest of the system somehow then you need an expansion tank to stop the valve. I cannot recommend you remove a saftey device unless I know your whole system. I'm sure the plumber put it there for a reason, and it's going off for a reason. Hot water expansion is one of the most power forces in nature. If your valve doesn't pop something else will. What is its setting?
 
It is set at 100. Also, I think it is actually on the cold water line on the outside shower. The water dripping out of it is cold. I ran the hot water in the house and on the outside shower that the relief valve is attached to and the drip did not slow at all and the water coming out stayed cold. I then did the same thing with the cold water and the drip still did not slow at all.
 
So unless you've put a bad valve in, which is possible, your pressure is getting over 100 and the needle isn't resetting. Have you tried blowing the line out really good and then replacing it? It could be getting full of gunk and not resetting, but it shouldn't be drippng or going off. It's hard to say without seeing anything. But I can't tell you you can cap it off. Why not call a plumber?
 
I wonder if we are talking about the same thing because I don't have a needle. This is what I am talking about.20210405_181702.jpg
 
Can you put a pressure gauge on you outside spigot, it should tell you what your pressure is
at rest, then turn on the cold on a faucet that will tell you what you have when there is a demand
 
Okay, with no demand it registered about 60 on the outside spicket. I turned on the outside shower and it dropped to about 55.
 
It initially had this Star Water Syastems pressure regulator on it. I figured that it had gone bad since it was leaking so much nonstop so I replaced it with the same part from Lowes. It started leaking immediately so I figured that the part was cheap so purchased the more expensive adjustable one from Watt online. These are the pics of the original one and the one I replaced it with. The replacement one lasted like 6-6 months max.
 

Attachments

  • Screenshot_20210405-192432_Lowe's.jpg
    Screenshot_20210405-192432_Lowe's.jpg
    344.9 KB · Views: 9
  • Screenshot_20210405-192242_Samsung Internet.jpg
    Screenshot_20210405-192242_Samsung Internet.jpg
    389.4 KB · Views: 8
Any number of reasons. All it does is lower the pressure from the sytem to whatever hooks up to it. They do act as a check valve. Maybe they had a sprinkler hooked up to it and they wanted it to only use a little water. But that's really not the best use for that.
 
They may be using that as a thermal expansion control device, although some of those type valves are not listed by a testing agency so they’re not code approved for that purpose, others are.

Some come with a set pressure but are not always accurate. Some are adjustable.

If you remove it, install a pressure gauge on a hose bibb and monitor for a few days and also check it again once it gets hot. You’re in Tampa, gets hot.

I would also perform a thermal expansion test. You can look up how to do that.

It is in fact a pressure relief valve.

Here is a link to the Watts brand above.
https://images.thdstatic.com/catalog/pdfImages/29/29b01d85-7d11-508c-a40d-164c365777ee.pdf
 
Last edited:
The regulator he took off was not a relief valve. He put a relief in its place. Neither will work being upside down, for very long anyway.
 
It initially had this Star Water Syastems pressure regulator on it. I figured that it had gone bad since it was leaking so much nonstop so I replaced it with the same part from Lowes. It started leaking immediately so I figured that the part was cheap so purchased the more expensive adjustable one from Watt online. These are the pics of the original one and the one I replaced it with. The replacement one lasted like 6-6 months max.


Thank you
 
Last edited:
Thank you
He’s calling it a pressure regulator but it’s a relief valve.. The foreign manufacture has a different interpretation of what we call a relief valve. Read the literature of how the valve operates. It’s a relief valve.

Read the link I posted. It’s the same type valve.,
 