Question - Expansion Tank on Hot Water Heater

Plumbing Forums

Help Support Plumbing Forums:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

MichaelB

New Member
Joined
Dec 9, 2019
Messages
4
Reaction score
0
Location
Montgomery, AL
I recently developed a pin hole on the top of my expansion tank at my hot water heater. I had a friend of the family come replace it. He put the new one on but did not adjust the pre-charged pressure in the tank. Ever since then, I have noticed a notable increase in water pressure in my house. Both toilets actually refill approximately 5-7 seconds faster than before and seem to make a louder noise when shutting off. I can hear a noise in one bathroom as soon as the toilet is flushed that seems to be coming from the wall. I also notice the increased pressure in the sinks, but this is easily controlled becasue of the faucets. I did not have any of these issues before the expansion tank was replaced.

Could the change in pressure be the result of the new expansion tank pressure not being adjusted or am I just missing something? If it is, is this something that can be easily fixed? I obviously do not want to have any pipe issues if at all possible.

Thanks for any help or insights.
 
That's quite a coincidence I'd say.
Should have no affect on your systems normal pressure.

I would suggest you take any pressure off from the water side of your expansion tank and charge the air pressure to closely match you water system pressure.
If you don't know what your water pressure is, you can pick up a pressure gauge that's made to hook up to a hose connection and connect to your silcock or washing machine hose valve.

The air correct pressure maximizes the volume of air in the tank that will be compressed when the water expands.
 
That's quite a coincidence I'd say.
Should have no affect on your systems normal pressure.

I would suggest you take any pressure off from the water side of your expansion tank and charge the air pressure to closely match you water system pressure.
If you don't know what your water pressure is, you can pick up a pressure gauge that's made to hook up to a hose connection and connect to your silcock or washing machine hose valve.

The air correct pressure maximizes the volume of air in the tank that will be compressed when the water expands.

What all has to be done to properly charge the air tank to the correct pressure? Is something that can be done easily?
 
Yes it's relatively easy.
There are many videos on it. Here's one.

I don't want to confuse you but he method the Watts guy describes is not getting all the pressure off the water side since you still have the hot water pipe full of water.
In other words, every 2.3 feet of water above the tank represents 1 psi. So if for example you had a 2 story house you could still have say about 7 PSI exerting pressure on that tank.
Depending on how yours is piped you may be able to avoid that discrepancy. So feel free to post a picture showing the piping around the expansion tank and heater.
I would just estimate the amount of water pressure is still on that tank and add that amount to my air pressure.
 
Yes it's relatively easy.
There are many videos on it. Here's one.

I don't want to confuse you but he method the Watts guy describes is not getting all the pressure off the water side since you still have the hot water pipe full of water.
In other words, every 2.3 feet of water above the tank represents 1 psi. So if for example you had a 2 story house you could still have say about 7 PSI exerting pressure on that tank.
Depending on how yours is piped you may be able to avoid that discrepancy. So feel free to post a picture showing the piping around the expansion tank and heater.
I would just estimate the amount of water pressure is still on that tank and add that amount to my air pressure.


Thanks
 
In my research for better video I read a lot of Watts comments /replies to peoples questions.
Apparently if a tank is over pressurized with air you could experience a momentary pressure surge above your normal pressure.
For example, if your water pressure was 50 psi and the air was set to 60 psi, expansion due to heating the water would allow that water to rise to 60 psi before expansion could take place.So when you open a faucet you could be seeing it going from 60 psi down to 50 psi for a few seconds or so, depending on the size of the tank.
Just for the hell of it, check the air pressure first.

EDIT: So maybe that plumber did pressurized it, at some point, at a much high pressure.:eek:
 
Last edited:
Or you might have a pressure reducing valve on the incoming water supply, which has malfunctioned or needs adjusting.
 