Recirculating Pump or Point of Use tank?

Plumbing Forums

Help Support Plumbing Forums:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.
Why all the confusion and discussion of flow rate and pressure changes.????
A recirculation loop simply puts the source of hot water closer to the point of use.
 
FROM the guys a TACO PUMPS



Benjamin Needham,

Taco has responded to the request you submitted on Taco-HVAC.com.

From: Benjamin Needham
Message: Ok so, Assuming the pump was sized based off of a design flow of approximately 1GPM... The head loss in your system would be ~ 0.5Ft If I plot out your system curve overlaid with the 007 pump curve, the actual expected flow would be ~ 4GPM 40 feet of 3/4 inch type L copper will hold ~ 1.016 Gallons 1.016Gal/(4 Gal/Min) ~ apprximitly 15 Seconds Provided the assumptions are correct.
To respond, please click here. Do not reply to this email

their you have it
approx 15 seconds for da hots wadder to be at the faucet
 
FROM the guys a TACO PUMPS
Benjamin Needham,

Taco has responded to the request you submitted on Taco-HVAC.com.

From: Benjamin Needham
Message: Ok so, Assuming the pump was sized based off of a design flow of approximately 1GPM... The head loss in your system would be ~ 0.5Ft If I plot out your system curve overlaid with the 007 pump curve, the actual expected flow would be ~ 4GPM 40 feet of 3/4 inch type L copper will hold ~ 1.016 Gallons 1.016Gal/(4 Gal/Min) ~ apprximitly 15 Seconds Provided the assumptions are correct.
To respond, please click here. Do not reply to this email

their you have it
approx 15 seconds for da hots wadder to be at the faucet
Not that this info, from Taco has anything to do with the issue you guys are debating about, but I feel compelled to point out that it's incorrect.
They are using 40 feet for the system curve, which is considerably less than what it actually is. 40 feet was(I believe) the single pipe line distance. (Not the entire loop with fittings.)
But like I said, I don't think the amount of time it took the hot water to reach the faucet, with a recirc system, was an issue anyway.
 
It’s like Payton place here. THIS IS SUCH A FIRST WORLD PROBLEM! Any pump will work. I’m soooo tired....
 