Hey all, new to the forum.

I recently purchased a house and would like to switch from well to city water. The house is on 6 acres and is about 850 ft from the main/meter. Since it is heavily wooded it may even be 1000-1100ft if I have to go straight to the road, turn 90 and run 200-250 feet to the main/meter. The tap and meter is 5/8 currently but can be switched out for a fee. The house is a 4 bath with 3 additional sinks. I'm in Florida so freezing is not an issue and the line only needs to be about 18 inches in the fairly sandy ground. From what I remember in speaking with the water dept, the main pressure is about 65psi.

My wife likes her water pressure so of course my first concern is pressure loss over the course of the 850-1100 foot run. Different charts online lead you to believe that a 3/4 inch line would only be dripping out water by the end of this run and a 1 inch run would not be much better. The first two plumbers I had out did not even mention upsizing from 3/4 inch until I mentioned pressure loss and even then seemed to play it off as no big deal. Both suggested 20ft sections of 3/4 inch Sch40. Can someone help me make a decision on pipe size? I just don't believe 3/4 inch is going to cut it.

Secondly, I was hoping to make a one piece run of PEX from the main to the house but it looks like Sch40 is the most commonly used down here and has been recommended by every plumber I've spoken to. The larger diameter and longer length PEX seems ridiculously overpriced compared to Sch40 of the same diameter. What price can I expect to pay for 1000-1200 feet of PEX in the size I would need?

Thank you for any help,
Richard



__________________
kcautodoc is offline  
 
Reply With Quote Quick reply to this message
Old 10-31-2013, 05:23 AM   #2
chukar
Senior Member
 
Join Date: Feb 2013
Location: Reno area, NV, have worked in AB, BC
Posts: 108
Liked 19 Times on 17 Posts

Default

It depends on more then just basic house usage are you going to want to run lawn hydrants off it, what about lawn sprinklers. I am on 1/2 acre, my water service is 1" from the meter to the house, and 3/4" in the house. IPC 2009 says the minimum water service pressure is 15psi, if you have lower pressures then I would look at upsizing your line perhaps to 1-1/4". When figuring what you want for service piping consider your needs today and down the road. If you wanted say in door fire protection sprinklers. I would say a 2" service.

If you have the volume of water you can add a booster pump later, to the house system.



__________________
chukar is offline  
 
Reply With Quote Quick reply to this message
Old 10-31-2013, 08:06 AM   #3
camaroderrick73
Senior Member
 
camaroderrick73's Avatar
 
Join Date: Apr 2013
Location: Sacramento, California
Posts: 152
Liked 30 Times on 29 Posts
Likes Given: 1

Default

I agree.. I would bring the volume to your house and if you need more pressure use a booster pump. The difference between 1 in and 2 in PVC is pennies in the long scheme. You need greater volume for pressure higher in the house. My house is 1.25 PVC. And my main that feeds 2 houses is 2 in. Overkill for your one house yes. But why not?

__________________
camaroderrick73 is offline  
 
Reply With Quote Quick reply to this message
Old 11-03-2013, 06:38 AM   #4
kcautodoc
Junior Member
 
Join Date: Oct 2013
Posts: 3
Default

I think I'm going to go with the 2". The price difference does seem to be small. I may try to increase the tap size as well. I can increase from 5/8 to 1 inch for about $350 dollars and it should more than double the flow rate. I am hoping the quote I get from the last plumber will be low enough that I don't decide to do it myself. Thank you for the help.

I also have a large pool and it would be nice to have a 2 inch pipe somewhere close to fill that thing up next year since it will need to be drained for resurfacing at some point soon.

__________________

Last edited by kcautodoc; 11-03-2013 at 06:41 AM.
kcautodoc is offline  
 
Reply With Quote Quick reply to this message
Old 11-03-2013, 08:30 PM   #5
Nukedaddy
Junior Member
 
Join Date: Oct 2013
Location: St. Louis, IL
Posts: 6
Liked 2 Times on 1 Posts

Default

I would agree with 2 inch, and you may save a bit using a lighter schedule as 65 psi is no great strain. Do consider a flushing hydrant at the house end. They look like miniature fire hydrants, but when opened give full flow for the purpose of flushing settled solids from the line, plus a possible high volume flow source for fire protection outside the house.

__________________
Nukedaddy is offline  
 
Reply With Quote Quick reply to this message
Old 11-03-2013, 11:55 PM   #6
johnjh2o
Senior Member
 
johnjh2o's Avatar
 
Join Date: Jul 2011
Location: Melbourne, Florida
Posts: 2,678
Liked 464 Times on 365 Posts
Likes Given: 330

Default

Quote:
Originally Posted by Nukedaddy View Post
I would agree with 2 inch, and you may save a bit using a lighter schedule as 65 psi is no great strain. Do consider a flushing hydrant at the house end. They look like miniature fire hydrants, but when opened give full flow for the purpose of flushing settled solids from the line, plus a possible high volume flow source for fire protection outside the house.
Never use any PVC pipe less then SCH 40 for water lines.
__________________

John

johnjh2o is offline  
phishfood Likes This 
Reply With Quote Quick reply to this message
Old 11-04-2013, 07:55 PM   #7
kcautodoc
Junior Member
 
Join Date: Oct 2013
Posts: 3
Default

I think I will need to go with the schedule 40. I was speaking to another plumber who told me that during the tourist season they crank up the pressure for the increase in water usage and on Mondays when the new crowds are getting settled in the pressure can get to nearly 110psi.

I'll look into the hydrant too. That will certainly help with filling the pool too.

__________________
kcautodoc is offline  
 
Reply With Quote Quick reply to this message
Old 11-05-2013, 06:30 PM   #8
Nukedaddy
Junior Member
 
Join Date: Oct 2013
Location: St. Louis, IL
Posts: 6
Liked 2 Times on 1 Posts

Default

While it is true that sch40 is the most common water line, and likely I would prefer it for my own, it is not the only code approved wall thickness. PVC SDR 21 and 26 pipe are both cold water rated at 100 and 200 psi, respectively. In particular, SDR26 is a common SDR type for water mains used by the water district.



__________________
Nukedaddy is offline  
 
Reply With Quote Quick reply to this message
Reply


Quick Reply
Message:
Options

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Slip Lining for house main cadillac1960 General Plumbing Help 0 10-03-2013 02:55 PM
Size of Septic System Question cover Septic Tanks 3 07-18-2013 07:23 AM
Tub Spout Pipe Type Mac Plumbing Building Code 2 01-26-2013 12:18 AM
1923 Old Main House Trap Clogged and Inaccessible MarkMark Drain and Sewer Cleaning 6 02-08-2012 09:47 PM
What Type of Diverter? nrdo Showers and Tubs 1 01-03-2011 10:56 AM

Newest Threads

LATEST SPONSOR DEALS