Old 10-13-2013, 08:56 AM   #1
confused
Junior Member
 
Join Date: Oct 2013
Posts: 5
Default Gas water heater

I need to replace a natural gas water heater that is inside a modular home. It has no door on the "alcove" it is located in. There is plenty of room for a regular water heater not a direct vent one to be installed. The home has been added on to before and is clearly not mobile. Can't a regular water heater be installed? Why is this any different than a regular home at this point?



__________________
confused is offline  
 
Reply With Quote Quick reply to this message
Old 10-13-2013, 12:19 PM   #2
johnjh2o
Senior Member
 
johnjh2o's Avatar
 
Join Date: Jul 2011
Location: Melbourne, Florida
Posts: 2,559
Liked 397 Times on 318 Posts
Likes Given: 253

Default

It cannot be installed in a enclosed area with out supplying combustion air. A lowered door would work.



__________________

John

johnjh2o is offline  
 
Reply With Quote Quick reply to this message
Old 10-13-2013, 01:09 PM   #3
Caduceus
Senior Member
 
Caduceus's Avatar
 
Join Date: Apr 2011
Location: Pittsburgh, PA
Posts: 932
Liked 197 Times on 143 Posts
Likes Given: 115

Default

I guess I'm also a little confused, too. The "alcove" is open and has no door where the existing tank sits, right? Is it visible and not in a closed, confined space? You kinda give the impression that it may be in a closed, built-in space, so some clarity is needed as John and I had the same impression. Your question is "can a regular water heater be installed?" and it seems that you already have a regular water heater in place, so what doubts are you having that a matching replacement cannot be installed?
I think that there is also some confusion about the type structure you live in. You say it's a modular home, but also state that it is clearly not mobile. A modular home is not a mobile home. It is simply a house that was made from complete prefabricated sections and put together like building blocks. It has never been mobile and is treated just as a normal house would be.

__________________
Caduceus is offline  
 
Reply With Quote Quick reply to this message
Old 10-13-2013, 05:04 PM   #4
confused
Junior Member
 
Join Date: Oct 2013
Posts: 5
Default

The house was a double wide but after it has been added onto it is just a house to me.
The area where the heater is had a panel on the front covering the tank. The panel has been taken off and thrown away several years ago so the heater can be seen when in the laundry room. It has 3 walls around it but a regular heater will fit with the necessary 1" clearance around it. The vent pipe is straight up through the roof. The tank leaked and I have to repair the floor if I am going with a regular heater should I cover the hole under it the one used for intake on a sealed combustion? Do I need a higher vent pipe?

__________________
confused is offline  
 
Reply With Quote Quick reply to this message
Old 10-13-2013, 05:48 PM   #5
Caduceus
Senior Member
 
Caduceus's Avatar
 
Join Date: Apr 2011
Location: Pittsburgh, PA
Posts: 932
Liked 197 Times on 143 Posts
Likes Given: 115

Default

What type of tank leaked and what type of tank do you want to replace it with? I know that you want to replace it with a "regular" tank, but it is unclear what you mean by a "regular" tank. There are gas fired, standard flu or gas fired power vented flu or electric or tankless gas fired or tankless electric or an indirect water heater connected to a boiler. To any person, any one of these could be considered a regular tank.
Also, maybe a few pictures would help to answer your questions.

__________________
Caduceus is offline  
 
Reply With Quote Quick reply to this message
Old 10-13-2013, 07:53 PM   #6
confused
Junior Member
 
Join Date: Oct 2013
Posts: 5
Default

The water heater that is in there now is a sealed combustion unit. I want to replace it with http://www.homedepot.com/p/GE-40-Gal-Tall-6-Year-36-000-BTU-Natural-Gas-Water-Heater-GG40T06AVG01/100013742?N=c1tz#.UlrzUSR4MhM
Attached are some pictures also note that the tank is leaning due to the floor I have to fix

__________________
confused is offline  
 
Reply With Quote Quick reply to this message
Old 10-13-2013, 09:07 PM   #7
johnjh2o
Senior Member
 
johnjh2o's Avatar
 
Join Date: Jul 2011
Location: Melbourne, Florida
Posts: 2,559
Liked 397 Times on 318 Posts
Likes Given: 253

Default

All new gas water heaters under 50 gal have sealed combustion chambers.

__________________

John

johnjh2o is offline  
 
Reply With Quote Quick reply to this message
Old 10-13-2013, 09:44 PM   #8
confused
Junior Member
 
Join Date: Oct 2013
Posts: 5
Default

What I meant was direct vent.

__________________
confused is offline  
 
Reply With Quote Quick reply to this message
Old 10-14-2013, 12:33 AM   #9
Caduceus
Senior Member
 
Caduceus's Avatar
 
Join Date: Apr 2011
Location: Pittsburgh, PA
Posts: 932
Liked 197 Times on 143 Posts
Likes Given: 115

Default

No, do not install a standard gas fired atmospheric water heater on a flu designed for a direct vent water heater. A direct vent heater flu is designed to use the combustion air from the outside. There are safety and corrosion risks if you use the same flu. Your best bet is to use another direct vent water heater. I know they cost more, but you would need a complete repipe of the flu to accommodate another style of tank.

__________________
Caduceus is offline  
 
Reply With Quote Quick reply to this message
Old 10-14-2013, 02:48 AM   #10
confused
Junior Member
 
Join Date: Oct 2013
Posts: 5
Default

I wasn't going to use the same flu. I was going to fix the floor and cover the hole there and use new flu pipe used for atmospheric gas water heater. I will most likely have a plumber redo the flu I just wanted to see if any body has done that and if it will work. In my mind without the tank being sealed and able to get air and with a flu for an atmospheric heater everything should work. I of course have co detectors in the laundry room because the furnace is in there also and no bedrooms are close. In your opinion will it work with a new floor and flu?



__________________
confused is offline  
 
Reply With Quote Quick reply to this message
Reply


Quick Reply
Message:
Options

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Water heater feed pipe shot. and now i have to replace my whole heater. chucksrt Water Heaters and Softeners 1 05-20-2013 01:14 AM
Water coming out of water heater power vent stevemachine Water Heaters and Softeners 6 12-23-2012 03:36 PM
Water in bottom of heater tank - and - hot water in cold lines SteveRiley Water Heaters and Softeners 14 11-09-2012 12:17 AM
Tankless Hot Water Heater, Noritz N0751M Will Not Heat Water iceundersiege Water Heaters and Softeners 6 04-03-2012 03:21 AM
Water heater connection to boiler domestic hot water coil gillric Water Heaters and Softeners 2 11-11-2011 11:16 AM