Old 05-21-2013, 05:24 PM   #1
Truelight
Junior Member
 
Join Date: May 2013
Posts: 4
Default pressure tank issues

Facts: low pressure 20 psi. We had water logged pressure tank. Changed tank. Water has not gone into tank. Still only 20 psi. Did not install check valve. We have a submersible pump. If I turn off power to pump pressure holds at 20. If I leave power on but close the shut off valve after guage, pressure stays at 20. Do you have any ideas? Should I have put in a check valve? Thanks



__________________
Truelight is offline  
 
Reply With Quote Quick reply to this message
Old 05-21-2013, 07:49 PM   #2
johnjh2o
Senior Member
 
johnjh2o's Avatar
 
Join Date: Jul 2011
Location: Melbourne, Florida
Posts: 2,629
Liked 446 Times on 350 Posts
Likes Given: 293

Default

I don't understand your statement that the water has not gone into the tank. Is it that the pressure won't build beyond 20 psi? Or is it going above 20 psi then drop after the pump turns off.



__________________

John

johnjh2o is offline  
 
Reply With Quote Quick reply to this message
Old 05-21-2013, 08:39 PM   #3
Truelight
Junior Member
 
Join Date: May 2013
Posts: 4
Default

I can lift the tank easily so I know there is no water in it. Pressure does not go above 20

__________________
Truelight is offline  
 
Reply With Quote Quick reply to this message
Old 05-21-2013, 10:20 PM   #4
johnjh2o
Senior Member
 
johnjh2o's Avatar
 
Join Date: Jul 2011
Location: Melbourne, Florida
Posts: 2,629
Liked 446 Times on 350 Posts
Likes Given: 293

Default

For some reason your pump isn't pumping. Is the pressure switch working? Check to see if you have power on the pump side of the switch.

__________________

John

johnjh2o is offline  
 
Reply With Quote Quick reply to this message
Old 05-21-2013, 11:38 PM   #5
Truelight
Junior Member
 
Join Date: May 2013
Posts: 4
Default

The pump runs continually because it never goes above 20 psi

__________________
Truelight is offline  
 
Reply With Quote Quick reply to this message
Old 05-21-2013, 11:41 PM   #6
johnjh2o
Senior Member
 
johnjh2o's Avatar
 
Join Date: Jul 2011
Location: Melbourne, Florida
Posts: 2,629
Liked 446 Times on 350 Posts
Likes Given: 293

Default

If the pump is running then you have a pump problem or a major leak in the line between the pump and the tank.

__________________

John

johnjh2o is offline  
 
Reply With Quote Quick reply to this message
Old 05-21-2013, 11:54 PM   #7
RichardHilliard
Member
 
RichardHilliard's Avatar
 
Join Date: May 2013
Posts: 30
Liked 9 Times on 8 Posts
Likes Given: 2

Default

What is your voltage?

The tank ,did you purchase a pressure tank or a galvanized tank? If you have a pressure tank make sure that the air in the bladder is 2 pounds less then the cut in pressure.

Check for leaks most likely in the casing

__________________

I had a hole in my pocket, I guess that is where my plans fell through.
Do not let "I've always done it this way" stop you

RichardHilliard is offline  
 
Reply With Quote Quick reply to this message
Old 05-22-2013, 04:49 PM   #8
Truelight
Junior Member
 
Join Date: May 2013
Posts: 4
Default

Ok i think I might have a leak between my

well pump and house. At the well house I have
2 faucets, 1 on either side of what I think is a

check valve. In my basement I have a shut off.


My pump runs continually at 20 psi. How can I
test to see if there is a leak?

__________________
Truelight is offline  
 
Reply With Quote Quick reply to this message
Old 05-22-2013, 09:38 PM   #9
RichardHilliard
Member
 
RichardHilliard's Avatar
 
Join Date: May 2013
Posts: 30
Liked 9 Times on 8 Posts
Likes Given: 2

Default

Turn power off to the pump pressure maintains 20 pounds= no leak or a bad gauge. If there is a leak between the pump and pressure tank it will go to zero pounds. Leak after house shutoff the pump should be able to pump up to 40 pounds or whatever your cutoff point is set.

240 volt submersible pump will not pump up to cutoff pressure if there is less than 240 /220 volts. Check your voltage to make sure you have 220/240 volts. Check your pressure switch too.

A pressure tank with bladder will only hold between 7-10 gallons of water. Your galvanized tank was a holding tank and not a pressure tank.

This may be the time to bring in an experienced plumber to test things for you.

It is extremely difficult to learn pumps on a forum. When it takes years to learn



__________________

I had a hole in my pocket, I guess that is where my plans fell through.
Do not let "I've always done it this way" stop you

RichardHilliard is offline  
 
Reply With Quote Quick reply to this message
Reply


Quick Reply
Message:
Options

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Pressure tank issue Help jterry Pumps and Wells 8 03-05-2013 12:33 PM
Pressure Tank kmarine0120 Pumps and Wells 2 02-03-2013 06:10 PM
Issue w/ well pump, pressure tank or pressure switch??? pmoney1983 Pumps and Wells 2 10-27-2012 01:48 PM
Will Increasing Pressure Tank Size, Increase Pressure? TxBuilder Pumps and Wells 8 07-13-2012 05:18 AM
pressure tank ebeveridge Pumps and Wells 5 07-13-2011 03:37 PM