Default two 1/2" lines feeding one 3/4" supply line?

Hello,

I am in the process of installing a new Manabloc pex manifold. I am doing home runs on each appliance in the kitchen, 2 bathrooms, utility room , and mud room, which are all centrally located near the utility room where the manifold is being installed.

The problem comes with a master bath that has a 3/4" supply going to it. All of the piping is not accessible (buried below sub floor from above, hidden above spray foam from below). Furthermore, it is a decent run to the master bath, 30' or so. So supplying hot water on a shower home run and then getting out of the shower and supplying hot water to the sink on a home run is a lot of waste, sending it over in one supply is preferable.

With all that being said my question is can I use 2 of the ports on the manifold to feed into one of the 3/4" supply lines for that bath? The math says that two 1/2" lines (.39 sq in) is just a tad smaller in volume than one 3/4" line (.44 sq in).

My concern is not the volume, rather it is the circuit looping back on itself. Maybe it's a non-issue due to equal pressure, or maybe there is some other possible problem with this setup that I don't know about. I wanted to get advice before I did it.

Thanks,
Josh



__________________
jkinder is offline  
 
Reply With Quote Quick reply to this message
Old 02-05-2013, 09:09 PM   #2
Beni
Member
 
Join Date: Jun 2011
Location: San Francisco, Ca
Posts: 99
Liked 15 Times on 14 Posts

Default

Well if the old piping is copper then the difference is .17" sq area for pex (actual inside dia) to .50" sq area for copper (type M). So for the same pressure drop you would need three Pex lines. Using multiple lines is fine BTW.

Pex of a given size has a smaller inside diameter due to a thicker wall of the tubing. While the PEX folks will say 1/2" pex is equal to 1/2" copper, that's not quite true. Pex uses insert fittings. So a 1/2" pex tee for example will have about a 3/8" waterway at the tee. Compared to copper or steel where the fitting waterway is the same diameter as for the pipe. So PEX automatically has a built in flow restriction. Thats the main reason the PEX folks use a manifold system as PEX does not really scale up 1 to 1 if piped as a conventional system. Using the manifold system overcomes that limitation...

So to equal a 3/4" copper pipe use at least three 1/2" PEX lines...



__________________
Beni is offline  
phishfood Likes This 
Reply With Quote Quick reply to this message
Old 02-06-2013, 12:47 PM   #3
jkinder
Junior Member
 
Join Date: Feb 2013
Posts: 2
Likes Given: 1

Default

Makes sense. Thanks for confirming that multiple lines will suffice.

You are correct about the I.D. I hadn't thought of that. Although I get some of that pressure back due to no 90 degree elbows that are inherent using copper.

Thanks again!

__________________
jkinder is offline  
 
Reply With Quote Quick reply to this message
Old 02-06-2013, 02:08 PM   #4
speedbump
Water well and pump tech
 
speedbump's Avatar
 
Join Date: Jan 2010
Location: Riverview, Florida
Posts: 950
Liked 56 Times on 53 Posts
Likes Given: 14

Default

Maybe another thing to consider is the friction loss of three 1/2" pipes as opposed to one 3/4" line.

speedbump is offline  
 
Reply With Quote Quick reply to this message
Old 02-06-2013, 11:15 PM   #5
Beni
Member
 
Join Date: Jun 2011
Location: San Francisco, Ca
Posts: 99
Liked 15 Times on 14 Posts

Default

Actually the pressure drop is not that bad. Your only flowing 1/3 of the total flow and weather 3 lines or 300 the pressure drop for a given flow rate will be about the same as for a single pipe. The flows add but the pressure loss or friction loss per foot is the same. That is, it does not get added across parallel runs, only flow rate does.

__________________
Beni is offline  
 
Reply With Quote Quick reply to this message
Old 02-07-2013, 12:15 AM   #6
stevemachine
Senior Member
 
stevemachine's Avatar
 
Join Date: Jul 2012
Location: edmonton, alberta
Posts: 789
Liked 90 Times on 78 Posts
Likes Given: 92

Default

Quote:
Originally Posted by speedbump
Maybe another thing to consider is the friction loss of three 1/2" pipes as opposed to one 3/4" line.
Agreed. Maybe not a huge difference but something to keep in mind. Depends, if all I had was 1/2 I'd probably just run that instead of buying 3/4.


__________________

If you don't learn something new everyday at work, it's not even worth going.

stevemachine is offline  
 
Reply With Quote Quick reply to this message
Reply


Quick Reply
Message:
Options

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Any point in 1" supply if water heater is 3/4"? rgeorgejr General Plumbing Help 2 03-13-2012 07:08 AM
2 Condos Two 3/4" Feed Lines - Now One mortym General Plumbing Help 6 07-06-2011 01:24 PM
Adjustable "Metric" and "SAE" wrenches? havasu Plumbing Tools and Equipment 3 04-12-2011 06:58 PM
Pex water line - connect to 1/2" or 3/4" source SnoSheriff General Plumbing Help 1 03-21-2011 01:47 PM
Vice President Joe Biden or Jeff Dunhams "Walter" SilverBack4Jack General Discussion 5 01-30-2010 12:53 AM