I'd appreciate any comments you all might have about this product. It's got lots of positive recommendations on Amazon.

http://www.gasflex.com/

http://www.gasflex.com/htms/english.htm

If I were to use this, it would be to connect a gas grill. I'd connect to an existing T in the rafters in my garage (currently used to supply gas to run a [non-existent] space heater - capped at the valve). I'd use a gas valve at the T, attach this stuff and run it on the underside of a covered walkway from house to garage, then down a 4x4 supporting the covered walkway. A second gas valve, and a gas grill quick connect would be attached. The run down the 4x4 would be inside a piece of PVC to protect against physical damage.

Recommendations appreciated. This is in Houston, Texas. I've been reading the code but am unsure if this pipe is to code.
 
Last edited:
Folks, I didn't get any responses to my query, and that's understandable given that this product doesn't have wide use or distribution in the USA.

I decided to go ahead with the flex pipe and completed the installation for my gas grill. If anyone is interested, I'll post it in the project forum with reference to this thread.

Cheers.
 
Flexible gas pipe is dangerous, prone to leaking, easily damaged, susceptible to lightening strikes (even the ones that claim otherwise), and will put you and your family at risk of injury and/or death.

Other than that, it is great stuff.
 
I am going to have to disagree. There is no more risk to lightning strike then galvy or black iron. It is more flexible in earthquake areas. And if installed and fused right pe pipe is the way to go
 
Only issues I've ever heard of with csst is easily damaged. If you hit it with a screw or something it'll punch right through, haven't heard of any issues regarding lightning myself up where I live. If installed properly should never leak. They put them in houses and bbq lines in Alberta and there hasn't been any issues. Just my two cents
 
...There is no more risk to lightning strike then galvy or black iron...
You are correct that it is no more susceptible to a strike than sch40 steel, but it is MUCH more prone to catastrophic failure as a result. The thin tubing does not hold up against the high current imposed as well as sch40 steel.

If a house were in an area that never gets lightning, then I guess it would be okay, but I would still not put it in my house. Not with my family. One township in Oklahoma is even asking all plumbing contractors in the area to report all homes with CSST gas tubes to the building official's office and the fire department. You have to ask yourself why they would be so concerned. Maybe it is because Edmond Oklahoma had six homes burn to the ground within a six month period. All were a direct result of CSST tubes blown out by lightning.

The attached graph illustrates the danger. Notice how much more energy is required to cause similar damage to sch40 steel. This is from the link below to Hawkeye Home Inspections. They also reference one of the homes destroyed in Edmond Oklahoma with photos. The CSST tubing was blown out but the steel pipe in the home was just fine.

In just "one" trail, the plaintiff was awarded over $1m because of blown out CSST from lightning.
http://claims-management.theclm.org/home/article/over-1-million-for-csst-case

This next is from Peekskill, NY in Westchester County:
http://ecode360.com/6430565

§ 422-17 Legislative findings; purpose; scope.
[Amended 2-22-1993; 10-22-2007 by L.L. No. 8-2007]

A. Legislative findings.
(1) The Common Council finds that prohibiting the use of corrugated stainless steel tubing (CSST), as approved by the New York State Uniform Fire Prevention and Building Code, would promote and protect the health, safety, welfare and property of the citizenry of the City of Peekskill and is therefore in the best interest of the citizenry of the City of Peekskill. The Common Council further finds that, through a nationwide class action lawsuit filed and settled against the various manufacturers of CSST, CSST has been found to be unreasonably susceptible to damage from arcing by direct or indirect lightning strikes. A direct or indirect lightning strike can create holes, allowing gas leaks that can result in a fire or an explosion.

(2) The Common Council finds that on one occasion, a puncture hole was caused by the inherent defects of CSST, causing a fire to burn for at least two months. The Common Council further finds that, separate from and in addition to the real hazard of direct or indirect lightning strikes, the CSST has caused, on two separate occasions within only a two-month period in the City of Peekskill, actual leaks within concealed spaces resulting from puncture holes caused by nails used in routine construction applications as a result of the CSST being pulled through existing walls against nails protruding into those walls, or new nails being hammered or shot with a nail gun into walls where CSST is located. These serious occurrences are substantial evidence that CSST is unreasonably prone to leaks, fire hazards and actual fires in normal construction situations. The Common Council does not know if these problems are unique to the City of Peekskill or if they are pervasive problems throughout New York State, but the risk of injury or death and property damage that has been experienced in the City of Peekskill far outweighs any economic benefit that the installer may realize though the use of CSST. The Common Council further finds that puncture holes made to CSST by both professionals and homeowners pose a very real threat to life, health, safety and property.

(3) Through this legislation the City desires to encourage the use of galvanized or black iron pipe, which it finds to be the most puncture-resistant material available for such applications, and to prohibit the use of CSST.

B. Purpose. The purpose of this section is to provide minimum standards to safeguard life or limb, health, property and public welfare by regulating and controlling the design, construction, installation, quality of materials, location, operation and maintenance or use.

C. Scope. This chapter represents basic standards governing the installation of gas piping and gas appliance connections in buildings. These standards apply only to low-pressure (not in excess of 1/2 pound per square inch) gas piping systems in buildings extending from the gas meter outlet or regulators to the inlet connections of appliances and the installation of residential and commercial gas appliances supplied through such systems by bottled gas or public utilities. They are intended to cover the installation and tests of such systems for fuel gases, such as natural gas and liquefied petroleum and/or manufactured gas. They are not intended to cover systems or portions of systems supplying equipment engineered, designed and installed for specific manufacturing, production manufacturing, production processing and power-generating applications, such as large and high-pressure boilers, melting and treating furnaces, production ovens, etc. For piping in gas distribution system, in gas manufacturing plants, in gas compressing stations and in gas processing plants, consult the gas utility corporation. No permit shall be required for installation, removal or refilling of liquefied petroleum tanks as a regular continued supply to building.


So again I say:
Flexible gas pipe is dangerous, prone to leaking, easily damaged, susceptible to lightening strikes (even the ones that claim otherwise), and will put you and your family at risk of injury and/or death.

Other than that, it is great stuff.

A little more light reading:
http://www.dps.state.ia.us/fm/CSST_Flier.pdf
http://www.csstsafety.com/CSST-lightning.html
http://hawkeyehomeinspects.com/wp-content/uploads/2013/06/CSST-DANGERS.pdf
http://www.huffingtonpost.com/2011/12/22/csst-gas-tubing-fires-concern_n_1164512.html
http://www.nbcnews.com/news/investi...s-reignite-debate-over-gas-pipe-safety-n55006
http://ecmweb.com/bonding-amp-groun...corrugated-stainless-steel-tubing-csst?page=2
http://www.forthepeople.com/class-action-lawyers/csst-lawsuits
http://www.wikinvest.com/stock/Omega_Flex_(OFLX)/Lovelis_Titeflex_Inc
http://www.reliableremodeler.com/bl...ings-about-corrugated-stainless-steel-tubing/
http://www.propertycasualty360.com/2011/02/07/burning-down-the-house-latent-csst-danger-seen-for
http://www.inspectionnews.net/home_...edback-corrugated-stainless-steel-tubing.html
http://www.myfoxlubbock.com/news/lo...tainless-steel-tu/g8SWXnf_ZEK1ON-vnhrbDw.cspx
http://www.kctv5.com/story/20109399/kctv5-investigates-gas-line-fires
http://www.classaction.org/csst
http://www.nh.gov/safety/divisions/firesafety/news/20120730-gas-pipe-hazard.html
http://www.iapfc.net/CSST Position Statement (2).pdf
http://www.myfoxtwincities.com/story/22782602/csst-fire-risk-minnesota-homes-built-after-1989
http://philadelphia.cbslocal.com/20...osion-danger-from-certain-natural-gas-tubing/

Screenshot 2014-06-10 09.17.42.jpg
 
Or in short...

CSST gas tubes are the single most dangerous thing to come down the plumbing pike since the indoor water closet had nothing but a chamber pot with no vent.
 
CSST was just starting to be used when I retired. I had one experience with it and it wasn't good. It was used to pipe a gas home generator that was installed outside. The home owner was mowing his lawn when he bumped the line were it connected to the generator causing the joint to leak. That would have never happened if it was black iron or galvanized. The lawn mower being used was a push mower. My opinion is it's too fragile to be used for gas.
 
I had the CSST pipe installed with my pool addition, and for a few bucks more, the installer provided me a branch to run my NG barbecue. This was all buried 18" below grade and when it came out of the ground, it was converted to black pipe. I would not hesitate using it again.
 
I had the CSST pipe installed with my pool addition, and for a few bucks more, the installer provided me a branch to run my NG barbecue. This was all buried 18" below grade and when it came out of the ground, it was converted to black pipe. I would not hesitate using it again.
This is the first item in TracPipe's FAQ's. http://www.tracpipe.com/FAQ/

Did you have it in a conduit?
 
To be honest, I didn't pay much attention, since this was the contractor's responsibility. I do know this was not placed in any conduit.
 
I have used PE underground to a black riser that comes from the PE manufacture for a outdoor pool boiler. I have also used the larger PE pipe where we had to fuse it together. I do not think CSST is good for underground. I know the few times we used CSST in a house we had to run a ground to by pass it.
 
I made an error. The gas line they installed underground for my pool was PE tubing, not CSST. Sorry, my CRS must be coming back to replace my ADHD when I was thinking CSST instead of PE.
 
I made an error. The gas line they installed underground for my pool was PE tubing, not CSST. Sorry, my CRS must be coming back to replace my ADHD when I was thinking CSST instead of PE.

PE makes it all make sense. I was really wondering what yahoo would put CSST under ground. PE is great for underground gas. In most circumstances it can't be beat in my opinion.
 
First of all, the tubing I used was not CSST. It is a PE coated (inside and outside) aluminum tubing 16/12 in diameter. In use and code approved for more than 10 years in Australia and Asia.

Second, none of the run I made is concealed. With the exception of the run down the 4 x 4, all tubing is in the rafters or overhead in the walkway. The down run on the 4 x 4 is protected with Schedule 40 PVC.

I don't get the comments about leakage. There are exactly two flex tube connection points... both use compression fittings, both extensively leak tested... so why should this leak over any other join or connection?

As for lightning? This is connected to black pipe. It's 28 feet long. It's under my carport/walkway and in the rafters of my garage. If lightening strikes at all, it's going to be a messy proposition, energy calculations notwithstanding.

My run of flex pipe has a cut off valve at the source in the event anything untoward should happen. I just don't get the "sky is falling" responses from a couple of posters.

And again, I'll be happy to post photos of the install if anyone is interested.
 
First of all, the tubing I used was not CSST. It is a PE coated (inside and outside) aluminum tubing 16/12 in diameter. In use and code approved for more than 10 years in Australia and Asia...
Codes allow all sorts of things that are not ideal. Good codes and good plumbing often find themselves on opposite sides of the fence. Sharkbite fittings, Polybutylene, lead water pipes, S&D PVC for building sewers, and push fit angle stops are all great examples of code approved items that many trade professionals refuse to use. Tankless water heaters being all the rage in Europe and Japan was the same line of bull we were given that brought that faulty marketing and junk systems to the U.S. Sorry StrongEagle, just because it is popular somewhere else is not a selling point that matters.

I remember being told I should buy a Slim Whitman album because he sold more records than Elvis...in Europe. That said, I have not personally dealt with polyethylene coated aluminum. But based on what I have read, I am not impressed. It sounds cheap (quality wise) and precarious at best.


...Second, none of the run I made is concealed. With the exception of the run down the 4 x 4, all tubing is in the rafters or overhead in the walkway. The down run on the 4 x 4 is protected with Schedule 40 PVC...
Sch40 PVC breaks down when exposed to UV sunlight (even indirectly). It does not hold up against even low impact assault because it becomes so brittle with age and UV damage. Your gas tube may be a lot of things but it is not "protected".

...I don't get the comments about leakage. There are exactly two flex tube connection points... both use compression fittings, both extensively leak tested... so why should this leak over any other join or connection?...
Flexible tubing of any sort conveying any gas or liquid can move and be moved. This contributes to the risk of leaks at the compression fittings. Compression fittings are the most susceptible to leaks of all mechanical joints.
...As for lightning? This is connected to black pipe. It's 28 feet long. It's under my carport/walkway and in the rafters of my garage. If lightening strikes at all, it's going to be a messy proposition, energy calculations notwithstanding...
The lightning strikes that cause CSST blow outs can be up to or more than a half mile away. Your house does not have to sustain a direct hit.

...My run of flex pipe has a cut off valve at the source in the event anything untoward should happen. I just don't get the "sky is falling" responses from a couple of posters...
The valve only helps if you are standing there when it happens. You have obviously never experienced a midwest thunderstorm. Some places in the world measure lightning strikes by how many they get in a year. During a thunderstorm here, we measure ours in the hundreds per hour. This storm in the UK delivered 200 cloud to ground strikes per minute.:
http://www.telegraph.co.uk/topics/w...ightning-bolts-strike-during-superstorms.html

Hopefully the folks in Venezuela are not using any CSST tubes.:
http://io9.com/5871791/one-place-in-venezuela-gets-40000-lightning-strikes-per-night

The sky is falling is a perfect analogy if you are in it or have to deal with the aftermath. I must attribute your not seeing the gravity of the situation to the possibility you just haven't experienced it. If you had, you might feel differently.

Yes, I am wound a little tight on this topic. This is not about business or protecting the trade from DIY'ers or unlicensed hacks. This is about public safety and lost lives. I mean no disrespect to you StrongEagle. This is all based on my knowledge that faulty products get approved, used, abused, and as a result good people get hurt.
 
This is a classic multipipe.. In Europe is allowed use of this product, but there are a several restrictions of pose.. You should check the rules of your state.. Anyhow, this is an English brand.. We haven't this brand in Italy.. Every brand must respect the dwg certificate.. At least in Italy..
 