Old 09-07-2011, 11:40 PM   #11
Senior Member
 
Join Date: Apr 2011
Location: , Alberta
Posts: 746
Default

When i click on the picture i see the V on the left and somebodys feet on the right....

I percieve this picture as this.... To the left is the V ( the vent in room you refer to ) I then see a wye taken off in 2" and then reducing to 1 1/2 that is intended to pick up a tub. Further down the branch I see a 3" pipe that is doing a 135' change of direction to its primary branch... within code ( you dont count the wye fitting change of direction only fitting AFTER.. more about this in a minute ) I then see a 90' bend with a 3 x 2 Wye taken off of it and I assume this is going to pick up a Lav, which makes it a wet vent for the bathroom group. ( you are going to be taking a vent off of the top of the lav t-wye i assume also ? ) i then see the branch terminate to a End cleanout to serve the branch. Do i interperit this correctlly ?

codes differ by regions but here your setup would fail, here are the things that would fail.

1. the T wye ( or Sani-T ) that picks up the toilet is against code. it must be a wye as a t wye is illegal to use in ANY horizontal configuration.. you WILL absolutely get blockages in the pipe over time if you dont change this to a wye and a 45' fitting.

2. the 90' bends must be 2 45's ( some places im told allow for the use of long sweep 90's ) where i am 90s anr not to be used horizontally or on any vertical to horizontal ( horizontal to vertical is allowed )

3. As i assume ( hopefully corectlly ) the lav is vented then you are corerect to use 2" as it is the minimum size of a wet vent allowed to serve a Toilet BUT, in Any wet vented configuration the Toilet must be the lowest fixture, this is so that when it is flushed it cannot syphon off any p traps ( as we do this here we will take the tub drain off of the 2" for the lav using a 2 x 1 1/2 wye, or a 2 x 2 wye in the case of a shower... we are not allowed to take seperate branches off of the 3" line that serves the bathroom group )

to answer your question Yes you could run 2" till after the p trap and then reduce to 1 1/2 as most tubs are set up to accept an 1 1/2 fixture outlet pipe, but it would be easyer to run it all in 1 1/2.

I would take a 45 off of the branch coming into the room and aim straight for the Toilet ( looks like there is enough room to work ), then before the Toilet install a 3 x 2 wye ( pointed in the direction of the feet in the pic ) this would be the Wet vent. I would then Install a 2 x 1 1/2 wye pointed in the direction of the tub ( knowing that i can still use a 45 or a 22 or the throw of the trap to get it exactlly where i need it if need be ), and I would run the 2" wet vent to the lav ( which would be tied to a 1 1/2 vent serving the entire bathroom group ).. I would install a 2" barret cleanout with an access panel to access it in the 2" pipe serving the lav so I could cleanout the wet vent if needed, and i would not install other cleanouts ( such as the one in the floor ) knowing that a clog in the tub could be remedy'd with a plunger and a blocked 3" I could lift the Toilet for access ( legal here in residential installations, but not commercial )

The current venting configuration you have ( even assuming the lav IS vented ) would be considered circuit venting, but would fail as the 3" and 2" and smaller traps must be seperatelly vented.

I will attempt to make a drawing to convey what i've said above, and upload it here.

Keep learning, there is much to plumbing that people dont realize.



LiQuId is offline   Reply With Quote
Old 09-08-2011, 01:57 PM   #12
Junior Member
 
Join Date: Sep 2011
Location: Bozeman, MT
Posts: 14
Default

Hi LiQuid,

thank you so much for your teaching/helping me. I couldn't appreciate this more!

I apologize for not having been entirely clear. The 2" you presume went to the lav actually is a branch-off to the kitchen - which is vented separately - but very far away.

You assumed correctly that the Wye to the left of my feet is a clean-out. I am not entirely sure where it goes after that... I assume it could make another bend to the vanity drain - which is vented - to the left of the toilet drain. If you look at the floor plan, you'll see that I have the fixtures in this order: Vanity, toilet, tub.

I uploaded the picture with my feet in it with better labeling:
http://reimann.files.wordpress.com/2011/09/drains-labeled.jpg
The vanity wet vent is located in the bottom left corner of the picture.


-------


Having pointed out that the 2" vent you were planning on using in your calibration isn't available, how would you vent the configuration? Looks to me like the two vents in the left of the picture are pretty close. Can't I somehow hook up to those? I would have to chip away at some concrete in that room as well.

Thank you so much again. I'm learning so much
 

Last edited by havasu; 09-08-2011 at 02:46 PM. Reason: click free viewing
snucky is offline   Reply With Quote
Old 09-08-2011, 11:08 PM   #13
Senior Member
 
Join Date: Apr 2011
Location: , Alberta
Posts: 746
Default

does the pipe past the cleanout ( labled "to vanity " ) continue in 3" and, if so does it pick up other fixtures or another stack ?

how do you upload an image? i got microsoft paint and drew out a configuration but it asks me for a url to post it.

IF the 3" is only there in 3" to be a cleanout access then I would say you should start at the first wye ( the tub ) and instead aim a 45 straight for the W.c. ( water closet ) . Between the w.c stub up and the 45 install a 3x2 wye ( the wye branch would point in the direction of the feet ), this is the lav wet vent and will also pick up the kitchen sink mentioned, it will require 3 45 degree fittings to sweep around the W.c. and terminate at the lav. and then almost immediatelly a 2x 1 1/2 wye ( which would point to the top right of the picture direction ) this 2 x 1 1/2 wye goes to the tub and MAY require 3 45 degree fittings to make the proper termination for the tub but I wager 2 would do it with the p trap sweep. Appologies if this explanation is difficult, It has been a long hot day re pipng in a boiler room.

Alternatelly, although NO LONGER ACCEPTED AS PROPER CODE. but it did work and was accepted for many years. you could take a 3 x2 wye off of the w.c branch and aim for your lav, this would properly vent the W.c. but not the tub although it was done for years assuming the 3" branch could supply suffician air to protect the trap of the tub.

Alternatelly and PROPER.

3x2 wye off of the W.c., aim for the lav. then install a 1 1/2 wye downstream of the tub p-trap and plan to bring a 1 1/2 " pipe into the wall behind the tub where you will tie it into the vent coming off the top of the lav ( IMPORTANT, must tie in above the rim of your sink and no lower, this is flood level rim AND since this vent is considered a flat vent you must take it off above the horizontal centerline of the tub branch, and must use drainage fittings i.e 45's and wyes and such ... no 90's ) This is a code clause that varies widely by region.

If I can figure out how to upload a picture I will do so... it would make things much easier.


Currentlly the biggest problem woth your configuration ( asside from the wrong use of fittings previously mentioned ) is that the tub is Un-vented and when the W.c. flushes it will syphon .

LiQuId is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are On
Refbacks are On



Latest Threads

Latest Reviews

MCC USA Inc. - CornerWrench

PASCO - Ez On Basket
Strainer - Brushed Nickel

PASCO - EZ On Basket
Strainer - Satin

Rheem - SolPak

Whirlpool - Du1300xtvq


Copyright © Group Builder, Inc - All Rights Reserved
Copyright ©2000 - 2012, Jelsoft Enterprises Ltd.
Content Relevant URLs by vBSEO 3.6.0
Network: Flooring Forum - Home DIY Forum - Garage Forum - Painting Forum