Cleanout Covers
The cleanouts generally are required to be the same size as the pipe they serve. Therefore if you have an 8 inch building sewer, you will have an 8 inch cleanout. You never really discussed the problem with the cleanout other than it was hard to find. That should not be a function of the size.
As a plumbing designer with over 30 years experience, and as a member of the ASME product standards commmittees for floor drains, trench drains, cleanouts and roofdrains, I typically specify the cleanout type and locate the cleanout outside of a building in an accessible area. If it is in a grassy or planting area, it should be brought to grade and a concrete pad should be poured around it to prevent damage from garden equipment or pedestrian traffic. Cleanout covers are generally a brass or PVC plug inside a sump that allows several inched of space between the pipe and the sump cover to allow for settling without affecting the pipe below. The cover should be rated for whatever traffic is anticipated, Pedestrian (light duty or medium duty) vehicle traffic (medium to heavy duty) depending on the type of traffic anticipated, If the cleanout is in an area where heavy delivery trucks, garbage trucks, or forklifts can drive over the cleanout cover, then a heavy duty or extra heavy duty top should be installed. When the cleanout is located in a paved area, the top elevation should be specified to match the grading and it should be set in a concrete pad anticipated for the traffic loading.
|