Default approved plumbing plan says 2"

Hello,
For our project we submitted a plumbing plan to the State with input on pipe sizes from our licensed plumber. The drain pipes for this remod of a commercial kitchen in an existing building are 2". The new remod will have a 3 compartment sink, floor drain and hand sink. State approved the plan for the 2" inplace pipe size. Now the plumber has started the work but he called in an inspector and this person says we need to tear up the floor and put in a new 3" line to connect to the 4" line going out to the city sewer. What the heck, help!!?? Anyone, thanks.


smalltowner is offline  
 
Reply With Quote Quick reply to this message
Old 01-20-2013, 04:37 AM   #2
Senior Member
 
Caduceus's Avatar
 
Join Date: Apr 2011
Location: Pittsburgh, PA
Posts: 663
Liked 63 Times on 48 Posts
Likes Given: 37

Default

The reason for the increase to 3" is because of the requirement of sizing for the floor drain as well as the 3 compartment sink and hand sink. A 2" drain line to handle this volume would be insufficient and cause problems. The plumber should know that a connecting floor drain above ground should be 3" (4" below ground at ground level) and the same size of pipe shall continue to the stack or sewer.
If your plumber is surprised by this situation, maybe you need to consult another plumber that is more familiar with plumbing code.
I don't mean to sound harsh, I just feel that this is just a simple part of plumbing that is known to licensed plumbers.
The state may approve the general plan, but it is the plumber's responsibility to apply the local codes to the installation to satistfy the inspectors. If he does not know what codes apply, then he should find out if he is qualified for that area.
UPC,IPC and others all require a 3" floor drain above ground for commercial install and the drain continues, undiminished in size, to the stack or building drain.


Caduceus is offline  
 
Reply With Quote Quick reply to this message
Old 01-20-2013, 04:38 AM   #3
Administrator
 
Chris's Avatar
 
Join Date: Jan 2010
Location: Wildomar, CA
Posts: 6,360
Liked 168 Times on 148 Posts
Likes Given: 16

Default

^ What he said...

Are your plans stamped, signed and approved for work? If so there is not a lot the inspector can do. If your are approved and what you are doing is to code he can not legally make you change it.

We run into this occasionally, sometimes even the inspector is right but if his district stamped and approved them then that is what goes.

Is your inspector with the same agency that approved your plans?

I would try to explain to him first that everything was installed per approved plan and let him know he needs to talk to the approver before you will do anything.

Edit: I typed this before ^ That post, If it will simply not work then now is a much better time to fix it right then when the job is done.

Edit again: Things must be different out here, the district that approves the plans is the same district that sends out the inspector which probably helps with things like this.
Chris is offline  
 
Reply With Quote Quick reply to this message
Old 01-20-2013, 04:40 AM   #4
Senior Member
 
Caduceus's Avatar
 
Join Date: Apr 2011
Location: Pittsburgh, PA
Posts: 663
Liked 63 Times on 48 Posts
Likes Given: 37

Default

I am assuming that the connecting floor drain is 3". If not, that is where the problems really started for the inspection.
Caduceus is offline  
 
Reply With Quote Quick reply to this message
Old 01-20-2013, 01:49 PM   #5
Junior Member
 
Join Date: Jan 2013
Posts: 5
Liked 1 Times on 1 Posts

Default

Quote:
Originally Posted by Chris View Post
^ What he said...

Are your plans stamped, signed and approved for work? If so there is not a lot the inspector can do. If your are approved and what you are doing is to code he can not legally make you change it.

We run into this occasionally, sometimes even the inspector is right but if his district stamped and approved them then that is what goes.

Is your inspector with the same agency that approved your plans?

I would try to explain to him first that everything was installed per approved plan and let him know he needs to talk to the approver before you will do anything.

Edit: I typed this before ^ That post, If it will simply not work then now is a much better time to fix it right then when the job is done.

Edit again: Things must be different out here, the district that approves the plans is the same district that sends out the inspector which probably helps with things like this.

This small town in the upper midwest has no local codes so we are governed by the state. Yes, the inspector is also employed by the state but he doesnt approve the plans. The plans are approved at a central office at the state capitol. Yes the plans are approved and we have a letter stating we shall now proceed with the work according to the plans then when done roughing in the plumber brings in the inspector to review and run pressure tests as needed.

The floor drain pipe is 2" and it is a take off from the main 4" line. More discussion would be appreciated, thanks.
smalltowner is offline  
 
Reply With Quote Quick reply to this message
Old 01-20-2013, 02:49 PM   #6
Junior Member
 
Join Date: Jan 2013
Posts: 19
Liked 5 Times on 3 Posts
Likes Given: 10

Default

The inspector usually holds all the cards. He is the one with the badge so it will be him that says yea or nay.

In my area an engineered plan certified by a "licensed" engineer that accepts full liability for the outcome would be required to trump the inspector. Plan reviewers miss things and do not have that authority.

It will be much cheaper to change it rather than fight it.
plbgbiz is offline  
 
Reply With Quote Quick reply to this message
Old 01-20-2013, 04:46 PM   #7
Senior Member
 
stevemachine's Avatar
 
Join Date: Jul 2012
Location: edmonton, alberta
Posts: 688
Liked 60 Times on 53 Posts
Likes Given: 15

Default

Well according to my code 2" pipe is good for 6 fixture units which you should be fine with what you have there. Unless everything is being wet vented. Then that's an issue. You can have a 2" floor drain, just it has to be vented is all. And everything else has to be individually vented but like plbgbiz said the inspector holds the card so what he says goes pretty well.


__________________
If you don't learn something new everyday at work, it's not even worth going.
stevemachine is offline  
 
Reply With Quote Quick reply to this message
Old 01-20-2013, 05:26 PM   #8
Junior Member
 
Join Date: Jan 2013
Posts: 5
Liked 1 Times on 1 Posts

Default

Our State code under "load on drainage piping" subpart 2a: Values for intermittent flows: Fixture unit values for interrmittent flows from applicances and equipment which are specially designed for low water use, and used for retrofit in existing plumbing systems only, may be determined as follows: Discharge Capacity (gpm) 8-16 has 2 fixture units, 16-30 gpm has 4 units and 31 to 50 has 6 units. No mention of min. drain size is stated here, however, under new construction there is a complete list of fixture types, unit values and min. drain size on a chart. Our project is not new construction so we would fall under subpart 2a, correct?
smalltowner is offline  
 
Reply With Quote Quick reply to this message
Old 01-20-2013, 06:22 PM   #9
Senior Member
 
stevemachine's Avatar
 
Join Date: Jul 2012
Location: edmonton, alberta
Posts: 688
Liked 60 Times on 53 Posts
Likes Given: 15

Default

Sounds about right to me. If the building is existing then yes I would say it sounds like 2a would be about right
__________________
If you don't learn something new everyday at work, it's not even worth going.
stevemachine is offline  
 
Reply With Quote Quick reply to this message
Old 01-20-2013, 07:10 PM   #10
Senior Member
 
stevemachine's Avatar
 
Join Date: Jul 2012
Location: edmonton, alberta
Posts: 688
Liked 60 Times on 53 Posts
Likes Given: 15

Default

I would maybe just bring it to either the plumber or inspectors attention. Just be careful with the inspector cause those guys can make you life a living hell lol


__________________
If you don't learn something new everyday at work, it's not even worth going.
stevemachine is offline  
 
Reply With Quote Quick reply to this message
Reply

Quick Reply
Message:
Options

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Is Type L Soft/Coil Copper generally approved for in home plumbing amodoko General Plumbing Help 11 11-11-2012 02:32 PM
Unvented system y plan Matt24 General Plumbing Help 10 03-13-2012 12:03 AM
"Happy Easter" to my U.S. Plumbing `Colleagues` CHRISM General Discussion 5 05-02-2011 02:45 PM
Can someone recomend to me a good "homeowner plumbing snake" rustywrangler Plumbing Tools and Equipment 6 01-07-2010 02:15 PM




Content Relevant URLs by vBSEO 3.6.0