Default New plumbing vent question

Can I vent fixtures where they meet, or just before where their arm meets the main drain line?

Due to existing roof penetrations and stacks, it would be much easier to vent these fixtures on the top side of bathroom rather than on bottom side and running vent lines all the way around the bathroom back towards the top wall.





__________________
Bogucki is offline  
 
Reply With Quote Quick reply to this message
Old 11-13-2013, 01:38 PM   #2
Caduceus
Senior Member
 
Caduceus's Avatar
 
Join Date: Apr 2011
Location: Pittsburgh, PA
Posts: 930
Liked 192 Times on 138 Posts
Likes Given: 112

Default

I deleted my previous post because I may have misinterpreted your drawing and description of how you want to do the installation.
Looking at it in two dimensions it looks like you want to run the vents off of the main for the fixtures unless what we are really looking at are the vents above the main and going through the walls?



__________________
Caduceus is offline  
 
Reply With Quote Quick reply to this message
Old 11-13-2013, 02:03 PM   #3
Bogucki
Member
 
Join Date: May 2012
Posts: 57
Liked 1 Times on 1 Posts
Likes Given: 4

Default

This bath is on a second floor and I'm trying to tap into the existing roof penetrations. The wall behind the toilet is attic space, so I'm running the main drain right behind this wall in the attic. Normally I would vent the vanity and tub on their own wall, but in this situation I would have to bring the vents all the way around the tub and back towards the stack on the far left. If I can vent these fixtures behind the toilet side wall, it will make my vent runs about 8' rather than 20'.

The drawing is oriented as if you were laying on the ceiling looking down. Floor joists run parallel to drains and tub, terminating at the top wall so that I can run drain pipe right along the outside of this wall, in attic space.

__________________

Last edited by Bogucki; 11-13-2013 at 02:06 PM.
Bogucki is offline  
 
Reply With Quote Quick reply to this message
Old 11-13-2013, 05:39 PM   #4
johnjh2o
Senior Member
 
johnjh2o's Avatar
 
Join Date: Jul 2011
Location: Melbourne, Florida
Posts: 2,475
Liked 339 Times on 276 Posts
Likes Given: 220

Default

The way you have it drawn the vents for the tub and lav. are too far from the fixture.

__________________

John

johnjh2o is offline  
 
Reply With Quote Quick reply to this message
Old 11-13-2013, 05:54 PM   #5
Bogucki
Member
 
Join Date: May 2012
Posts: 57
Liked 1 Times on 1 Posts
Likes Given: 4

Default

How about venting here between the floor joists, closer to the traps?



__________________
Bogucki is offline  
 
Reply With Quote Quick reply to this message
Old 11-13-2013, 07:21 PM   #6
johnjh2o
Senior Member
 
johnjh2o's Avatar
 
Join Date: Jul 2011
Location: Melbourne, Florida
Posts: 2,475
Liked 339 Times on 276 Posts
Likes Given: 220

Default

A horizontal vent must be 6" above the flood rim of the fixture. That would be 42" above the floor.

__________________

John

johnjh2o is offline  
 
Reply With Quote Quick reply to this message
Old 11-13-2013, 08:06 PM   #7
Bogucki
Member
 
Join Date: May 2012
Posts: 57
Liked 1 Times on 1 Posts
Likes Given: 4

Default

Thanks John,

So a lav that is 36" above the floor would require a vent to be 6" above the flood rim before turning horizontally; making the vent turn at a minimum 42" above the floor. That definitely kills my hope of venting close to the attic side wall.

I guess that means I will have to vent each fixture in the wall they are on, meaning I will have to run the vents all the way back around the bathroom.

So I'll bring the lav vent up the wall 42" before turning across and then tie tub vent with it, then take that all the way around the bathroom walls and take it out a roof jack. Does that look proper? My major concern with this run is making sure I maintain .25" slope from end to end with no dips.



__________________
Bogucki is offline  
 
Reply With Quote Quick reply to this message
Old 11-13-2013, 08:10 PM   #8
johnjh2o
Senior Member
 
johnjh2o's Avatar
 
Join Date: Jul 2011
Location: Melbourne, Florida
Posts: 2,475
Liked 339 Times on 276 Posts
Likes Given: 220

Default

You got it. But to make it easier why not put the head of the tub and the sink on the same wall as the toilet.

__________________

John

johnjh2o is offline  
 
Reply With Quote Quick reply to this message
Old 11-13-2013, 08:28 PM   #9
Bogucki
Member
 
Join Date: May 2012
Posts: 57
Liked 1 Times on 1 Posts
Likes Given: 4

Default

Yes sir, I wish I could. The problem is that this bathroom has a sloped ceiling. It is part of a 1940's attic that was converted to living space many years ago.

The back wall is about 4' high, enough to accommodate a toilet and the back portion of the shower, but not tall enough to support a mirror/lav and shower head. The bottom wall, where the shower head and lav are going, is the stairwell wall and almost directly above it is the ridgeboard of the house, so I want to avoid making another roof penetration this high up the roof, although it would be much easier.

Preceding this, I had to rebuild the entire second floor since they utilized the original first floor 2x4 ceiling joists as floor joists for the second floor. I'm actually amazed how much wood will deflect before completely failing. This is what we found when we tore out dinning room ceiling; we knew we'd had no choice but to tear it all out and start over. And yes, those are scabbed 2x4's spanning over 12' supporting a bedroom.!



__________________

Last edited by Bogucki; 11-13-2013 at 08:31 PM.
Bogucki is offline  
 
Reply With Quote Quick reply to this message
Old 11-13-2013, 08:42 PM   #10
uplumb
Junior Member
 
Join Date: Nov 2013
Posts: 23
Default

It never ceases to amaze me what some people will do..



__________________
uplumb is offline  
 
Reply With Quote Quick reply to this message
Reply


Quick Reply
Message:
Options

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Help finding plumbing vent stack marc General Plumbing Help 8 11-23-2012 05:37 PM
Plumbing drainage and vent systems steveplank40 General Plumbing Help 1 06-22-2011 06:53 PM
vent question dlangdon50 General Plumbing Help 4 05-20-2011 01:51 AM
Plumbing Vent with Slip-on or No-Hub emcconne General Plumbing Help 1 01-22-2011 05:02 PM
another vent question bridgeboy General Plumbing Help 4 07-17-2010 10:55 AM