ohh, wow.... you could effectively vent thousands of DFU's .. no joke.
Its funny for me to say it but the 90 on the #" horizontal portion of the

bathtub vent is technically wrong, though I would be a gazillion dollars it doesnt clog. also "technically" you should have access to cleanouts if a vent is below flood rim, It must be piped as though it were a drain, And again.. must come off of the pipe whos trap it serves ABOVE THE HORIZONTAL CENTERLINE which, technically is impossiblle since you used 3" to vent.
you could have used 2" to achieve the same. how it is I would consider Trap evaporation my biggest concern... It will work, but is way overkill.
Edit:..... hmmm it is 2" isnt it ?? lol, my bad. you're good to go, change out the 90's for 45's add a barett C/o on each vent line and cover them with panels when you finish the wall.